Reznor F75 natural gas heater

I have been unable to get my garage heater going despite having two yahoos ($150) come and look at it. I have replaced the gas valve ($100) and the thermocoupler and pilot assembly ($30) I can keep the pilot lit but it will not kick in. what am I missing? I have also placed a new regulator on it ($40). The two wires that go to the thermostat are wired together so it should fire right up. Help me before I pull out the remaining hair on my bald head!
Reply With Quote
  #2 (permalink)  
Old 09-20-07, 09:38 PM
furd's Avatar
Member
 
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 4,214
There are several possibilities. Wanna send me a round-trip airline ticket and have me come out and troubleshoot it? I haven't worked on anything like that for close to thirty years but I'm pretty sure that with a few hours and maybe some new parts I could get it going.


Seriously, tell us everything that you know about your unit and what the two "yahoos" did and maybe someone here can offer a few suggestions.
Reply With Quote
  #3 (permalink)  
Old 09-21-07, 03:24 AM
Member
 
Join Date: Sep 2007
Posts: 11
reznor

the first guy said the gas was coming out too fast and put a regulator on it. He also sugested that I replace the thermocoupler and pilot assembly. I did that. The second guy said that the gas valve was bad so I replaced that. This thing still will not fire. I am able to light the pilot and it stays lit, but will not ignite the rest of the burners and start the blower fan.
Reply With Quote
  #4 (permalink)  
Old 09-21-07, 10:34 AM
furd's Avatar
Member
 
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 4,214
Do you have an instruction or installation manual for this unit?

Does this furnace have a blower in it? Is it a conventional forced air furnace or is it a wall furnace? Does it use a 24 volt control circuit or does it use a millivolt control?

Can you post some pictures? Close ups of the wiring and control systems would help.
Reply With Quote
  #5 (permalink)  
Old 09-21-07, 11:09 AM
Topic Moderator
 
Join Date: Aug 2007
Posts: 1,589
Quote:
Originally Posted by rootercycles View Post
the first guy said the gas was coming out too fast and put a regulator on it. He also sugested that I replace the thermocoupler and pilot assembly. I did that. The second guy said that the gas valve was bad so I replaced that. This thing still will not fire. I am able to light the pilot and it stays lit, but will not ignite the rest of the burners and start the blower fan.
Did you download the manual from Reznor like I suggested in the last thread? You're going to need the schematc and a voltmeter to see where the circuit to the gas valve is open.
Reply With Quote
  #6 (permalink)  
Old 09-24-07, 08:22 PM
Member
 
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 929
I'm confused. You had two techs look at your furnace and gave you a diagnosis and they didn't replace the parts? You did?
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are Off


All times are GMT -7. The time now is 07:09 PM.

Find Qualified
Local Contractors

Select Service:

Enter Zip:

 

Content Relevant URLs by vBSEO 3.2.0