| If you swap the two zone valve powerheads, and the problem follows the powerhead, you know it's not the t'stat... If the valves are close to each other, you can just swap the wire from the #1 terminal between the valves. If the upstairs thermometer operates the downstairs valve, you know the t'stat is good. But 99% of the time, it's the powerhead. The reason the boiler fired up when you removed #1 and switched to manual open is because you removed the wrong wire. #1 is the wire from the thermostat to the heatmotor that opens the valve. #2 is the 'common' wire to both the heat motor and the endswitch. #3 is the endswitch wire that fires up the boiler. If you remove this wire, the boiler will not start when you manually open the valve. __________________ Never worry about theory as long as the machinery does what it's supposed to do. LL |