Steam cycle too long. How to limit?

I have an old house (1905) with a single pipe steam system that replaced an old "snowman" coke furnace. The boiler's about 8 years old, and it heats well. I have found though that when it runs for more than about 10 minutes, especially when stone cold, the radiators fill with sloshing water, even though they've been tipped to make sure water flows back down. Left unattended, water can shoot out the steam valves.

I quickly learned that just letting the heat run was unproductive, and often led to cleaning up water on the floor. What works best is letting it run for about 8-10 minutes, then turning it off for 2 minutes to let the water drain back down. Doing this, the house heats up more evenly and more quickly. Of course, this means running to the programmable thermostat every 8-10 minutes to fiddle with it.

Is there something I can put between my thermostat and my furnace to regulate this for me?
Reply With Quote
  #2 (permalink)  
Old 11-20-08, 06:01 PM
NJ Trooper's Avatar
Topic Moderator
 
Join Date: Oct 2006
Location: NJ - south of 'The Yellow Zone'
Posts: 5,479
I'm not a steamhead... we need one of them on this one ...

I know a question to ask though:

Are the pipes insulated ?
__________________
Never worry about theory as long as the machinery does what it's supposed to do. LL
Reply With Quote
  #3 (permalink)  
Old 11-20-08, 07:50 PM
Member
 
Join Date: Nov 2008
Location: Boston, MA
Posts: 2
Quote:
Originally Posted by NJ Trooper View Post
I know a question to ask though:
Are the pipes insulated ?
They all were once insulated with asbestos, like the old snowman, but now about 50% of them are insulated. I have some more to put on, which sounds like my weekend project now!
Reply With Quote
  #4 (permalink)  
Old 11-21-08, 04:57 AM
Member
 
Join Date: Nov 2005
Location: USA
Posts: 1,754
Plenty of good steam guys in Boston. Start calling around. The system shouldn't be that wet. Might need new main vents, might be some issues with the piping, etc.
Reply With Quote
  #5 (permalink)  
Old 11-21-08, 03:20 PM
NJ Trooper's Avatar
Topic Moderator
 
Join Date: Oct 2006
Location: NJ - south of 'The Yellow Zone'
Posts: 5,479
I know if ya post a picture or ten, I for one would find something to pick on ! I'm good for that ...

free account / Image hosting, free photo sharing & video sharing at Photobucket / upload there / post link here ...
__________________
Never worry about theory as long as the machinery does what it's supposed to do. LL
Reply With Quote
  #6 (permalink)  
Old 11-21-08, 03:33 PM
plumbingods's Avatar
Topic Moderator
 
Join Date: Apr 2008
Location: Manch-vegas, New Hampshire
Posts: 2,150
First off, steam pipes must be insulated and with fiberglass, not rubber insulation.

It sounds like you are getting a lot of surging going on in your boiler. You may need to drain it down, put some steam boiler liquid in and let it boil for a while, skim off the impurities and then make sure it is clean. I have not done this in years, so the exact process is a little fuzzy to me, but I am sure we can help you find something to read about it if you cannot.

Has this boiler always worked like this? If so, there could also be some piping issues.
__________________
Please read user profile.

Remember...
"Can't never did a damn thing but try always did"

Mark
Reply With Quote
  #7 (permalink)  
Old 11-21-08, 08:19 PM
Member
 
Join Date: Jul 2007
Location: Pennsylvania
Posts: 1,081
As stated skim the boiler. You don';t need chemicals to do this just skim as per the manucaturers directions. When skimming does not work skim again. Also as stated insulate those mains.
See link
Steam FAQ
Reply With Quote
Reply

Tags
cycle, limit, steam

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


All times are GMT -7. The time now is 08:21 PM.

Find Qualified
Local Contractors

Select Service:

Enter Zip:

 

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.2.0