Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Hydronic Heating System
nguyen1953
04-04-02, 07:12 PM
My boiler keeps overheating, with the hot water being released through the pressure relief valve. I've replaced the air expansion tank and the pressure relief valve, but the overheating continues. The thermostats for the boiler are set at the appropriate temperatures.
Need some help on pointing out where the problem may be.
Thank you.
HVN
Need some help on pointing out where the problem may be.
Thank you.
HVN
TheZman
04-04-02, 07:56 PM
What PSI reading are you seeing on your altimeter gauge ?
You should see 12-15 PSI for a cold boiler (for a typical two story house). A hot boiler will read 18-25 PSI.
If you see values much higher than these, you need to adjust your pressure regulator which supplies water to your boiler from the cold water line.
You should see 12-15 PSI for a cold boiler (for a typical two story house). A hot boiler will read 18-25 PSI.
If you see values much higher than these, you need to adjust your pressure regulator which supplies water to your boiler from the cold water line.
nguyen1953
04-04-02, 08:08 PM
Thank you. I have another question. Where is this altimeter located? There is nothing from the cold water supply line to the boiler where I can see this altimeter.
Thank you again for your help.
HVN
Thank you again for your help.
HVN
TheZman
04-05-02, 04:34 AM
HVN,
The altimeter is a essentailly a pressure gauge (typically 3" diameter) that is graduated from 0-50 or 0-60 PSI and it should sit right on top of the boiler by itself.
Thanks
TheZman
The altimeter is a essentailly a pressure gauge (typically 3" diameter) that is graduated from 0-50 or 0-60 PSI and it should sit right on top of the boiler by itself.
Thanks
TheZman
nguyen1953
04-05-02, 05:18 AM
TheZman, thanks a lot! Yes, the altimeter has been going up past 30. I see that there is a Watts regulator on which it says "Set 12-15, Range 10-25". I guess this is what I would need to replace to solve the problem.
Thanks again for your help! Have a good day!