Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Boiler Won't Fire


Adk_Ben
11-02-09, 08:16 PM
I have a Smith Oil fired boiler that I found in the reset position. Upon reset it runs for about 20 seconds, but does not seem to fire.


I do have oil
Oil is getting to the nozzle and the nozzle seems clear.
Unfortunately I did not have a new nozzle.
It doesn't seem to fire even for a moment.


Any thoughts would be appreciated.

Ben


NJ Trooper
11-03-09, 02:24 AM
Could be lotsa things Ben... transformer, primary control, Cad cell... to name a few. When was the last time it was serviced?

Don't keep pushing the reset, and if you have pushed it a whole bunch of times, make sure you tell the tech that you did... you might have a bunch of unburnt fuel in the chamber now...

I think you want to call a tech.

Adk_Ben
11-03-09, 09:47 AM
Could be lotsa things Ben... transformer, primary control, Cad cell... to name a few. When was the last time it was serviced?

Don't keep pushing the reset, and if you have pushed it a whole bunch of times, make sure you tell the tech that you did... you might have a bunch of unburnt fuel in the chamber now...

I think you want to call a tech.

I'd like to try a few things first. I plan to replace the nozzle with a new one this afternoon. Hopefully, I will have some luck there.

I've also been advised to check the alignment of the electrodes and to also check to be sure that voltage is getting to the electrodes.

I'm hopeful that this is a simple fix and will certainly call a tech. when I've exhausted my bag of tricks.

Any and all help / advice is appreciated.

Ben


formula74
11-03-09, 08:08 PM
How many times did you push the reset and try to fire it?

I agree with NJ Trooper that this sounds like it should be looked at by an oil burner tech. Just tinkering with it to make it fire will at best result in an improperly adjusted burner that is going to soot up your equipment and waste fuel or it could be straight up dangerous.

The nozzle should be replaced with the proper one for the equipment. Just looking at it isn't good enough. The nozzle size, spray angle and cone type must be correct as well as the pump pressure.

A combustion analysis should also be performed as part of the service.

Adk_Ben
11-04-09, 06:12 AM
I changed the nozzle last night, but that did not seem to fix the problem Calling a tech. today.

Ben

GRIMKNOTME
11-04-09, 04:55 PM
How many times did you push the reset and try to fire it?

Once is plenty 2 X STOP.

I agree with NJ Trooper that this sounds like it should be looked at by an oil burner tech. Just tinkering with it to make it fire will at best result in an improperly adjusted burner that is going to soot up your equipment and waste fuel or it could be straight up dangerous.

The nozzle should be replaced with the proper one for the equipment. Just looking at it isn't good enough. The nozzle size, spray angle and cone type must be correct as well as the pump pressure

A nickle isa ole term setting between gap.



A combustion analysis should also be performed as part of the service.

I changed the nozzle last night, but that did not seem to fix the problem Calling a tech. today.

Ben

Check for build up on end of nose cone clean off then retry.


Read all and reply

Adk_Ben
11-09-09, 06:26 PM
In case anyone is interested, it was a bad transformer. Service tech stated that the boiler looks good, including the electrode alignment and cleaning... score one for me!!

formula74
11-09-09, 06:35 PM
Good to hear it's back up and running. Now you can put this one in your bag of diagnostic tricks for next time :D I'd say the burner tech visit was well worth it.

cheers