Air Conditioning - Water Source Heat Pump (Climatemasters) problem.
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Water Source Heat Pump (Climatemasters) problem.
zalmai
10-26-09, 12:46 PM
I have a condo-Apartment in a High-rise building built in 2003. My condo is equipped with 2 water source AC unit (ClimateMasters with CMX/DMx control) 1 upstairs and one down stairs.
Here is the Problem:
The compressor at the downstairs unit shuts down after a few seconds after start up. The fan keeps running. You can hear the compressor starting up then shutting off.
The filter is brand new.
Is there a quick fix without calling the tech.
Thanks for the help.
Here is the Problem:
The compressor at the downstairs unit shuts down after a few seconds after start up. The fan keeps running. You can hear the compressor starting up then shutting off.
The filter is brand new.
Is there a quick fix without calling the tech.
Thanks for the help.
Houston204
10-26-09, 05:10 PM
Remove the panel and inpect the LED for the trouble code and post it here. Be Careful 240 volts is present in this panel.
You may have to use a screwdriver to jumper the 2 test terminals on the circuit board before a trouble code is displayed.
You may have to use a screwdriver to jumper the 2 test terminals on the circuit board before a trouble code is displayed.
Houston204
10-26-09, 05:38 PM
This pic might help...
http://i151.photobucket.com/albums/s160/Houston204/ClimateMasterTranquility.jpg
http://i151.photobucket.com/albums/s160/Houston204/ClimateMasterTranquility.jpg
zalmai
10-27-09, 04:55 PM
Houston204,
Thanks for the instructions. I did the test and here is what I got:
Flash code 2 = 2 quick flashes, 10 sec. Pause.
then
the compressor kicked in for 10 seconds or so
then
the compressor switched off and the LED started fast flashing (locked).
Then I turned the power off and did a regular restart. (no test mode this time)
The LED light stayed on
Then again the compressor kicked in for 10 seconds or so
Then the compressor switched off
The LED light started flashing slow.
I hope this helps...
Thanks again..
Thanks for the instructions. I did the test and here is what I got:
Flash code 2 = 2 quick flashes, 10 sec. Pause.
then
the compressor kicked in for 10 seconds or so
then
the compressor switched off and the LED started fast flashing (locked).
Then I turned the power off and did a regular restart. (no test mode this time)
The LED light stayed on
Then again the compressor kicked in for 10 seconds or so
Then the compressor switched off
The LED light started flashing slow.
I hope this helps...
Thanks again..
Houston204
10-27-09, 06:47 PM
Your high pressure switch lockout is probably due to low water flow. Is the pump or valve that supplies water to your heatpump getting power?
Post the model number of your unit.
This is what the GS , GR, GC manual states for 2 flashes...
High pressure switch:
When the high pressure switch opens due to high refrigerant pressures, the compressor relay is de-energized immediately since the high pressure switch is in series with the compressor contactor coil. The high pressure fault recognition is immediate (does not delay for 30 continuous seconds before de-energizing the compressor).High pressure lockout code = 2Example: 2 quick flashes, 10 sec pause, 2 quick flashes, 10 sec. pause, etc.
http://i151.photobucket.com/albums/s160/Houston204/ClimateMasterGSGRGCwithCXMboard.jpg
Post the model number of your unit.
This is what the GS , GR, GC manual states for 2 flashes...
High pressure switch:
When the high pressure switch opens due to high refrigerant pressures, the compressor relay is de-energized immediately since the high pressure switch is in series with the compressor contactor coil. The high pressure fault recognition is immediate (does not delay for 30 continuous seconds before de-energizing the compressor).High pressure lockout code = 2Example: 2 quick flashes, 10 sec pause, 2 quick flashes, 10 sec. pause, etc.
http://i151.photobucket.com/albums/s160/Houston204/ClimateMasterGSGRGCwithCXMboard.jpg
zalmai
10-29-09, 12:44 PM
Hello again Houston204,
The model # is 30XG0N0B1.
Here is what I think is going on:
I came up with HP Fault-Code 2
There are 4 possible causes (According to Functional Troubleshooting Table).
1-Reduced or no water flow (very likely)
2-Water Temperature out of range in cooling (very unlikely)
3-Overcharged with refrigerant (very unlikely since the refrigerant is factory sealed and has not been touched)
Here is my question:
Is the water flow problem a building plumbing problem or is there a regulator in the unit that controls the water flow/pressure?
thanks again,
The model # is 30XG0N0B1.
Here is what I think is going on:
I came up with HP Fault-Code 2
There are 4 possible causes (According to Functional Troubleshooting Table).
1-Reduced or no water flow (very likely)
2-Water Temperature out of range in cooling (very unlikely)
3-Overcharged with refrigerant (very unlikely since the refrigerant is factory sealed and has not been touched)
Here is my question:
Is the water flow problem a building plumbing problem or is there a regulator in the unit that controls the water flow/pressure?
thanks again,
Houston204
10-29-09, 05:29 PM
The diagram shows a motorized valve between stat Y and heatpump Y. Some of my ClimateMaster diagrams show a pump here.
Since you are in California, I just assumed that this is a cooling lockout. If this is a heating lockout, it could be a low airflow problem.
Since you are in California, I just assumed that this is a cooling lockout. If this is a heating lockout, it could be a low airflow problem.
Jarredsdad
10-29-09, 06:37 PM
Fan keeps running, doubt is an HP fault in heat. Other Unit is working. As Houston said, is there a valve in the piping? Something has slowed/stopped water flow.
zalmai
11-01-09, 09:54 AM
Hello again,
So what is the best thing to do to get this thing fixed? Is there a valve to be replaced?
Thanks
So what is the best thing to do to get this thing fixed? Is there a valve to be replaced?
Thanks
Houston204
11-01-09, 11:27 AM
Locate the valve or pump that supplies water to your heatpump and verify that it is getting power when demand is present.
Post the make model of this device for futher assistance.
Pics might also help us help you.
If replacement of this device is required, you would be better served getting a licensed and insured company to replace it.
The potential damage that you can cause can easily be from the tens, to hundreds of thousands of dollars, if you attempt to replace a valve or pump in a high rise building.
Post the make model of this device for futher assistance.
Pics might also help us help you.
If replacement of this device is required, you would be better served getting a licensed and insured company to replace it.
The potential damage that you can cause can easily be from the tens, to hundreds of thousands of dollars, if you attempt to replace a valve or pump in a high rise building.
Houston204
11-01-09, 11:36 AM
Your building chief engineer would have the best recommendations for a company familiar with your building.
They probably wouldn't replace it themselves do to this liability issue.
If it is only a loose wire or minor electrical repair they may be of greater assistance.
They probably wouldn't replace it themselves do to this liability issue.
If it is only a loose wire or minor electrical repair they may be of greater assistance.
zalmai
11-04-09, 05:28 PM
Hello Houston,
The qualified tech worked on it today here is what happened:
My diagnosis was right and there is water flow problem.
The CXM controller is working properly.
The Temperatures at inflow and outflow are OK.
He vacuumed the inflow and outflow and some rusty water was drawn out of the coil.
The Problem did not fix
He did more vacuuming and more vacumming...
Still the problem did not go away
Here is his recommendation:
He thinks the flow regulator is stuck and not working
He says replacing the flow regulator is a major work. It will take him a couple hours to replace the regulator since it is silver welded. He said he also has to locate a climatemaster regulator which might cost around $300-$400 (parts only). He will also have to run acid through the coil and that will take couple more hours. The total will run around $1100 to $1500.
Does this sound right?
Please advise...
Thanks
The qualified tech worked on it today here is what happened:
My diagnosis was right and there is water flow problem.
The CXM controller is working properly.
The Temperatures at inflow and outflow are OK.
He vacuumed the inflow and outflow and some rusty water was drawn out of the coil.
The Problem did not fix
He did more vacuuming and more vacumming...
Still the problem did not go away
Here is his recommendation:
He thinks the flow regulator is stuck and not working
He says replacing the flow regulator is a major work. It will take him a couple hours to replace the regulator since it is silver welded. He said he also has to locate a climatemaster regulator which might cost around $300-$400 (parts only). He will also have to run acid through the coil and that will take couple more hours. The total will run around $1100 to $1500.
Does this sound right?
Please advise...
Thanks
Jarredsdad
11-04-09, 06:18 PM
No it doesn't sound right. A little heat and the flow reg is out. If the tech reads the manual, he can install a simple ball valve and manually regulate flow to climatemaster specs. Vac? If rusty water is being sucked out I think it would indicate no flow.
I have never vaced a water coil. Flow reg screwed up I can agree with. Prices are very high. Melting silver brazing and removing a fitting, $400 parts only? $10 ball valve, set and forget.
I have never vaced a water coil. Flow reg screwed up I can agree with. Prices are very high. Melting silver brazing and removing a fitting, $400 parts only? $10 ball valve, set and forget.
Jarredsdad
11-04-09, 06:22 PM
Acid clean is not a couple ours. 5 gallon bucket with biodegradable muratic acid solution. Submersible pump, pumps the solution through the coil. Takes maybe (at a strech) an hour. Smoke is blowing here...
zalmai
11-04-09, 06:32 PM
Hello Jarredsdad,
Today the Tech for his work charged me $200.
Just to let you know..
Thanks
Today the Tech for his work charged me $200.
Just to let you know..
Thanks
zalmai
11-04-09, 07:04 PM
Hello again Jarredsdad,
The heatpump climatemaster model # is 81630GNPKSCOK. Is there really a flow regulator welded on the inflow side as the Tech stated?
Thanks
The heatpump climatemaster model # is 81630GNPKSCOK. Is there really a flow regulator welded on the inflow side as the Tech stated?
Thanks
zalmai
11-05-09, 11:16 PM
Here is what the Chassis Serial # for my unit means:
816= Model Type Chassis
30=Unit Size
G=Voltage (208-230/60/1)
N=Options
P-Control CXM
K-6GPM Automatic Flow Regulator
S-No Water Valve
C-Copper Coax
O-Standard
K-Revision Level
So according to these numbers there is a 6GPM Automatic Flow Regulator and there is no water valve or secondary pump in this unit.
Now the question is "Is the Automatic Flow Regulator really bad? and Is it really welded?"
816= Model Type Chassis
30=Unit Size
G=Voltage (208-230/60/1)
N=Options
P-Control CXM
K-6GPM Automatic Flow Regulator
S-No Water Valve
C-Copper Coax
O-Standard
K-Revision Level
So according to these numbers there is a 6GPM Automatic Flow Regulator and there is no water valve or secondary pump in this unit.
Now the question is "Is the Automatic Flow Regulator really bad? and Is it really welded?"
zalmai
11-06-09, 10:22 PM
Here is some very interesting progress I made on water flow issue.
I wanted to get a second opinion so that I could be sure before spending the $1500 cleaning and replacing the water flow regulator. Here is what happened. I brought in an electrician to check the controller. The controller checked to work what it is supposed to do. Then we tuned off the inflow and outflow valves and opened the fittings. Then we pulled out the chassis. Then we got a bucket and released the inflow water valve into it. The high pressure water rushed out into the bucket. The only problem was the water is dirty black and full of sediments (sand and tiny metal particles). The water was so much polluted with sediments and metal that we had a hard time closing the valve (basically the sediments were ceasing the valve). The bottom 3rd the bucket is full of sediments. So the problem is the water coming into the system. It probably has already damaged the regulators, valves or what so ever inside.
So the conclusion is:
It is the HVAC water tower for the building that caused my unit to go bad.
I wanted to get a second opinion so that I could be sure before spending the $1500 cleaning and replacing the water flow regulator. Here is what happened. I brought in an electrician to check the controller. The controller checked to work what it is supposed to do. Then we tuned off the inflow and outflow valves and opened the fittings. Then we pulled out the chassis. Then we got a bucket and released the inflow water valve into it. The high pressure water rushed out into the bucket. The only problem was the water is dirty black and full of sediments (sand and tiny metal particles). The water was so much polluted with sediments and metal that we had a hard time closing the valve (basically the sediments were ceasing the valve). The bottom 3rd the bucket is full of sediments. So the problem is the water coming into the system. It probably has already damaged the regulators, valves or what so ever inside.
So the conclusion is:
It is the HVAC water tower for the building that caused my unit to go bad.