Thermostatic Controls - T8775C compatible with L8148J Aquastat?
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : T8775C compatible with L8148J Aquastat?
schellas
10-06-09, 01:13 PM
Hi,
I have a T8775C (digital round, power stealing) thermostat hooked up to a L8148J aquastat connected to my boiler. Most of the time the thermostat successfully communicates with the aquastat and the boiler/circulating pump kicks on when the temp. drops below the set point on the thermostat. However, from time to time (maybe 1x/week or so), the room temp will be below the set temp. and the boiler/circulating pump won't kick on. To resolve this, I usually have to lower the set temp well below the room temp. and wait a few minutes before raising the set temp. back up above the room temp...then the heat kicks on, usually.
The thermostat is approx. 4 yrs old and the aquastat was replaced 2 years ago for a different problem (circulating pump would go on but boiler wouldn't fire). As the L8148J is a millivolt circuit, could it be incompatible with the
T8775C as this is a "power stealing" thermostat?
Any help would be greatly appreciated.
Thanks!
I have a T8775C (digital round, power stealing) thermostat hooked up to a L8148J aquastat connected to my boiler. Most of the time the thermostat successfully communicates with the aquastat and the boiler/circulating pump kicks on when the temp. drops below the set point on the thermostat. However, from time to time (maybe 1x/week or so), the room temp will be below the set temp. and the boiler/circulating pump won't kick on. To resolve this, I usually have to lower the set temp well below the room temp. and wait a few minutes before raising the set temp. back up above the room temp...then the heat kicks on, usually.
The thermostat is approx. 4 yrs old and the aquastat was replaced 2 years ago for a different problem (circulating pump would go on but boiler wouldn't fire). As the L8148J is a millivolt circuit, could it be incompatible with the
T8775C as this is a "power stealing" thermostat?
Any help would be greatly appreciated.
Thanks!
Houston204
10-06-09, 05:23 PM
That is an unreliable thermostat. I recommend a Honeywell thermostat that requires batteries if you cannot supply a C (common) wire to your stat. A non-digital would also work.
http://i151.photobucket.com/albums/s160/Houston204/HonT8775digitalstat.jpg
http://i151.photobucket.com/albums/s160/Houston204/AuquastatL8148J.jpg
http://i151.photobucket.com/albums/s160/Houston204/HonT8775digitalstat.jpg
http://i151.photobucket.com/albums/s160/Houston204/AuquastatL8148J.jpg
schellas
10-06-09, 08:47 PM
Thank you for your response. I prefer digital display...might the Honeywell RTH5100B be more reliable than the T8775?
Please advise.
Thanks again!
Please advise.
Thanks again!
Jay11J
10-06-09, 09:33 PM
.might the Honeywell RTH5100B be more reliable than the T8775?
Yes, the RTH5100B will be a better t-stat.
Yes, the RTH5100B will be a better t-stat.