Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




diydiy
10-02-09, 02:30 PM
Here's what I have:

Trane XE1000 Heat Pump
Trane TWE060C5FC1 Air Handler
???? WTS0702(F) Heat Unit
Trane Thermostat (Weathertron - BAYSTAT240)

I am installing a Honeywell RTH7600 TouchScreen Thermostat

Closely following the manual and some tips online here is how I have wired the RTH7600:

WEATHERTRON HONEYWELL
BAYSTAT240 WIRE RTH7600

B black C
G green G
Y yellow Y
O blue O/B | W
- N/A jmp|-RC
R red jmp|-R
__________________________________

W white L3 | Aux
- N/A Y2 | E
- orange -
T brown -
F N/A -
Note: The layout is BAYSTAT240 - WIRE - RTH7600
(The forum doesn't keep my formatting unfortunately)

So the system seemed to be running fine and behaving ok except the other day I noticed that the outside compressor is running ALL the time. And it did not do this until I installed the new thermostat. So what could be wrong with how I wired the thermostat?


Jay11J
10-02-09, 06:57 PM
Can please redo on how you did it.

Example.

Old-------New
R----------R/Rc
C-----------C
G----------G


ect..

diydiy
10-02-09, 07:46 PM
Ok, here it is:

WEATHERTRON----------------- HONEYWELL
BAYSTAT240--------WIRE--------RTH7600

--------B---------------black-------------C
--------G--------------green-------------G
--------Y---------------yellow------------Y
--------O---------------blue--------------O/B | W
-------N/A--------------N/A---------------jmp|-RC
--------R----------------red---------------jmp|-R
__________________________________

--------W--------------white-------------L3 | Aux
--------N/A------------N/A---------------Y2 | E
--------N/A------------orange-----------N/A
--------T---------------tan(brown)-------N/A
--------F---------------N/A---------------N/A
Need some [CODE] tags in this forum so things stay formatted.


Jay11J
10-02-09, 08:12 PM
Everything is wired up correct.

Make sure the Y wire is not touching R.

If it still running, undo the Y wire and see if that stops the unit outside.

Also, Do you know what your KW rating on the air handler? Reason I asked is you don't have E wired up.

diydiy
10-02-09, 08:20 PM
Ok, I thought I had the wiring right. I'm wondering if the contactor is maybe acting up. It's 14 years old and original. I've replaced all the caps last year but thought the contactor was still ok. Maybe not.

Anyway, the air handler is rated at 6A. And the heater unit is 7kw.
It's a multi-stage heat. Heat pump and emergency strips.

Jay11J
10-02-09, 08:31 PM
You have on bank of heat strip? If yes, then you need to add a jumper between Aux and E on the T-stat.

if you have more than one bank, then you need to add the unused t-stat wire to E and go to the air handler and wire E to W2 at the air handler.

diydiy
10-02-09, 09:41 PM
I have one bank of strips so I'll add the jumper Aux to E.
I'm going to replace the contactor and that should fix the continuous compressor run problem.

Jay11J
10-03-09, 06:46 PM
Sounds like a plan. Let us know if you have anyy other questions.