Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Heat kicks on when set to cool


btpowell
09-24-09, 03:38 PM
I just installed a Honeywell 7600 and when set to cool, the heat kicks on from the heatpump/ac condenser. I have it wired as such: R-R with a jump to RC, G-G, Y-Y, B-C, O-O, and W-Aux with a jump to E. I also have a brown wire which is pushed back. If it is not wired correctly, how should it be wired?


Jay11J
09-24-09, 07:51 PM
I just installed a Honeywell 7600 and when set to cool, the heat kicks on from the heatpump/ac condenser.
You may need to go into setting #190 and change it to 1


I have it wired as such: R-R with a jump to RC, G-G, Y-Y, B-C, O-O, and W-Aux with a jump to E.
What was the make/model of the old t-stat? Reason I'm asking is the "B".

I also have a brown wire which is pushed back. If it is not wired correctly, how should it be wired?
What is your heating? (Gas or Electric?) Make and model as well on those.

btpowell
09-24-09, 08:17 PM
The old t-state was a GE and that is all I can tell you. Unfortunately, I threw it away a month ago before I installed this one (I previously installed the Honeywell 6400 that my wife purchased). I have gas heat and the condenser is a Fraser-Johnston. I have traced the brown wire to the B terminal on the condenser. Hope this helps a bit.


Jay11J
09-24-09, 08:27 PM
The old t-state was a GE and that is all I can tell you.
Okay, GE/Trane use B as common.

I have traced the brown wire to the B terminal on the condenser.
Is the brown wire on O/B at the t-stat?

btpowell
09-25-09, 02:31 PM
The brown wire is pushed back into the wall. The O wire is connected to the O terminal.

Jay11J
09-25-09, 09:46 PM
Have you gone into setting #190 and change it to 1 ? If you did, did that help?

btpowell
09-26-09, 01:36 PM
When switching the 0190 to 1 from from 0, the heat stiil kicks on. Other ideas/tips?

Jay11J
09-26-09, 08:19 PM
The gas burner on the furnace is running while the A/C is running?

What happens if you remove the wire from Aux/E?