Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Fan & compressor not running
markl
07-02-09, 12:18 AM
I have a Goodman heatpump model # CPLJ30-1B
I went out tonight for about 5 hours & when I returned home it was 83 in the house with the T stat set at 77, the inside fan was running but when I went outside the unit was not running.
I turned the unit off & turned it back on 1 hour later, when I went outside the unit wasn't running so I took a long screwdriver & gave the fan blade a nudge & it started to run, but I couldn't hear the compressor running & I wasn't getting any cold air from the duckwork, after standing next to the outside unit for awhile I could hear a humming sound that would last for a second or two every couple of minutes.
I'm looking for any suggestions as to what may have gone wrong & what & how to check it.
I don't have any experience with heatpumps but I do have some experience with auto AC & I'm ASE certified for refrigerants.
Thanks in advance for any assistance.
I went out tonight for about 5 hours & when I returned home it was 83 in the house with the T stat set at 77, the inside fan was running but when I went outside the unit was not running.
I turned the unit off & turned it back on 1 hour later, when I went outside the unit wasn't running so I took a long screwdriver & gave the fan blade a nudge & it started to run, but I couldn't hear the compressor running & I wasn't getting any cold air from the duckwork, after standing next to the outside unit for awhile I could hear a humming sound that would last for a second or two every couple of minutes.
I'm looking for any suggestions as to what may have gone wrong & what & how to check it.
I don't have any experience with heatpumps but I do have some experience with auto AC & I'm ASE certified for refrigerants.
Thanks in advance for any assistance.
dac122
07-02-09, 06:20 AM
I would begin by replacing your run capacitor. Its jprovides a boost of power to overcome the inertia needed to get your fan and compressor moving.
mattison
07-02-09, 06:28 AM
Sounds like you you have a capacitor that has went bad. Older Goodmans had that issue.
You'll have to power down the outside unit, open the service cabinet, remove the old capacitor "take a digital picture or make not of the wire locations". Take the capacitor to a motor shop, Grainger, Johnstone, HVAC supply store, etc... and have them match it up for you. Re-install it and repower it. Should work.
http://i37.photobucket.com/albums/e83/mattison67/sf219.gif
Dac beat me... :)
You'll have to power down the outside unit, open the service cabinet, remove the old capacitor "take a digital picture or make not of the wire locations". Take the capacitor to a motor shop, Grainger, Johnstone, HVAC supply store, etc... and have them match it up for you. Re-install it and repower it. Should work.
http://i37.photobucket.com/albums/e83/mattison67/sf219.gif
Dac beat me... :)
markl
07-02-09, 07:01 AM
Sounds like you you have a capacitor that has went bad. Older Goodmans had that issue.
You'll have to power down the outside unit, open the service cabinet, remove the old capacitor "take a digital picture or make not of the wire locations". Take the capacitor to a motor shop, Grainger, Johnstone, HVAC supply store, etc... and have them match it up for you. Re-install it and repower it. Should work.
http://i37.photobucket.com/albums/e83/mattison67/sf219.gif
Dac beat me... :)
I kind of had a feeling that might be what was wrong when I was able to get the fan to run by moving it with a screwdriver, but I wasn't sure one capacitor worked the fan & compressor.
Don't I need to discharge the capacitor before removing it?
How do I go about doing that? I really don't feel like getting zapped.
I downloaded a service manual & it mentioned to discharge it first.
This unit isn't real old, the house was built in 2004 & I've been in it since 2007.
You'll have to power down the outside unit, open the service cabinet, remove the old capacitor "take a digital picture or make not of the wire locations". Take the capacitor to a motor shop, Grainger, Johnstone, HVAC supply store, etc... and have them match it up for you. Re-install it and repower it. Should work.
http://i37.photobucket.com/albums/e83/mattison67/sf219.gif
Dac beat me... :)
I kind of had a feeling that might be what was wrong when I was able to get the fan to run by moving it with a screwdriver, but I wasn't sure one capacitor worked the fan & compressor.
Don't I need to discharge the capacitor before removing it?
How do I go about doing that? I really don't feel like getting zapped.
I downloaded a service manual & it mentioned to discharge it first.
This unit isn't real old, the house was built in 2004 & I've been in it since 2007.
dac122
07-02-09, 07:33 AM
Dac beat me... :)
You are clearly one of those hard-working moderators that doesn't just sip coffee and eat donuts. Sorry to have stolen your thunder. ;)
You are clearly one of those hard-working moderators that doesn't just sip coffee and eat donuts. Sorry to have stolen your thunder. ;)
markl
07-02-09, 12:02 PM
A big thanks guys, the problem is solved & you hit the nail on the head.
I purchased a new capacitor for $18 + tax & it only took a few minutes to install.
Thanks again.
Mark
I purchased a new capacitor for $18 + tax & it only took a few minutes to install.
Thanks again.
Mark