Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Trane XL19i
harveje
06-22-09, 03:15 PM
I have a Trane XL19i 5 ton split heat pump with strips, live in north east MS with a Vision Pro IAQ T stat. I want the first stage on A/C to run the max amount of time to get the moisture out of the air currently 95f 67 % humidity outside, 72f 57% humidity inside. Water is a constant drip on the drain and I have a dehumidifier running inside that I empty 1-2 times every 24 hrs. House has crawlspace with vapor barrier on ground, duct work is in attic. The unit is constantly switching low / high / low / high......and I know the switching is killing my electric usage. Any help is appreciated.
Thanks,
Jimmy
Thanks,
Jimmy
Jay11J
06-22-09, 04:01 PM
In the installer set up menu, what is 220, and 230 set to?
Is 370 set to 1?
379 set to 1?
Do you know if dehum from the EIM wired to BK on the air handler?
Is 370 set to 1?
379 set to 1?
Do you know if dehum from the EIM wired to BK on the air handler?
harveje
06-22-09, 06:23 PM
Thanks Jay,
220=1
230=2
370=1
379=1
wire form control box going to bk terminal on air handler jumper removed R-BK.
Thanks,
220=1
230=2
370=1
379=1
wire form control box going to bk terminal on air handler jumper removed R-BK.
Thanks,
Jay11J
06-22-09, 08:56 PM
Try 230 at 1, and see what happens.
Also maybe 690 to 1.
Also maybe 690 to 1.
harveje
06-23-09, 07:45 PM
Thanks Jay,
I changed them today and will wait a day or so to monitor the system
Thanks,
I changed them today and will wait a day or so to monitor the system
Thanks,
Jay11J
06-23-09, 07:57 PM
Yeah, let the t-stat readjust itself after a few days.