Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : a/c won't work
the5easons
06-12-09, 06:24 PM
Hi, I have a Janitrol Unit that is about 10 yrs old. It is an air to air w/ gas back-up unit. I know that when you run out of gas in the winter the air to air will not work until you fill back up with gas. Now my a/c will not work. The unit in the attic runs and you can hear it, but the outside unit/fan does not cut on, I took the cover off and pushed the contacts and it cut on fine as long as I held it. My question is will the a/c not cut on til the unit knows there is gas in it? Any help would be appreciated. Thanks!
Grady
06-12-09, 07:40 PM
Not having gas has nothing to do with the unit not running. Since this sounds like a heat pump, I've moved this thread to the Heat Pump forum. What is the model number of the outdoor unit? I have manuals on some of the older Janitrol equipment.
the5easons
06-12-09, 08:11 PM
Where do I find the model number? I have never had trouble with it as of now.
Thanks, Craig
Thanks, Craig
wirenut1110
06-13-09, 04:38 AM
You should test for 24 volts to the contactor coil in the condenser. The one you pushed in. For safety reasons, I don't recommend manually pushing in contactors.
If you have 24 volts then you probably have a bad coil. If you don't have 24 volts, then you need to check the t-stat or the wiring.
If you have 24 volts then you probably have a bad coil. If you don't have 24 volts, then you need to check the t-stat or the wiring.
the5easons
06-13-09, 08:51 AM
Goodman Manufacturing
Model number: CPKJ30-1AB
Serial: 9837525216
That coil is right behind the contacts, right? Is it all one unit?
Model number: CPKJ30-1AB
Serial: 9837525216
That coil is right behind the contacts, right? Is it all one unit?
the5easons
06-13-09, 09:27 AM
The Model number is CPKJ30-1AB
Goodman
Goodman
the5easons
06-14-09, 08:32 PM
Ok, I traced 24volts from the thermostat in the house to the unit in the attic, the chip board has 2 sets of contacts, 1 set coming from the thermostat on the top, and the set on the bottom of the chip board goes out to the outside unit. Well, I am getting good 24 to theto from the thermostat, but only 7 volts out of the bottom of the chip board. What is this chipboard called. Where do you get one? Thanks for any help. Craig
daddyjohn
06-23-09, 05:20 AM
furnace control board. Take a look here:
Furnace Control Boards (http://arnoldservice.com/control_boards.htm)
What is the model # of the furnace?
Furnace Control Boards (http://arnoldservice.com/control_boards.htm)
What is the model # of the furnace?