Air Conditioning - Condenser Not Kicking On
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Condenser Not Kicking On
aboilerfan
04-28-09, 05:49 PM
A couple of days ago, my A/C condenser stopped kicking on. The fan ran fine, but contactor was clicking. The condenser worked when I manually engaged the contactor. Replaced the contactor and everything worked fine.
Ran the A/C for a day and half, and now I am getting the same thing. I checked continuity and voltage on contactor and relay - everything looks good. I checked circuit board and fuse on air handler - good. No obvious damage (bulge, collapse) of capacitor -- I replaced that a couple of years ago, but I do not have a capacitor tester.
Any ideas?
Ran the A/C for a day and half, and now I am getting the same thing. I checked continuity and voltage on contactor and relay - everything looks good. I checked circuit board and fuse on air handler - good. No obvious damage (bulge, collapse) of capacitor -- I replaced that a couple of years ago, but I do not have a capacitor tester.
Any ideas?
dun11
04-29-09, 05:15 AM
Does the cond fan still run fine ?
aboilerfan
04-29-09, 05:25 AM
Condenser fan kicks on fine if contactor is manually pushed in.
dun11
04-29-09, 05:37 AM
Does the comp try to start ?
Is it hot ?
Is it hot ?
aboilerfan
04-29-09, 06:53 AM
Condenser does not try to start unless contactor is manually engaged -- manually push contactor in, it starts right up. Release the contactor and it stops immediately. It is getting 24v from thermostat, but it just clicks and does not engage.
Checked continuity and voltages on contactor and time delay relay, and everything looks good. Checked for blown fuse at circuit board on furnace/air handler - good.
Checked continuity and voltages on contactor and time delay relay, and everything looks good. Checked for blown fuse at circuit board on furnace/air handler - good.
dun11
04-29-09, 07:23 AM
OK to clarify, you get a good 24v from transformer to coil of contactor when there is a call for cooling, all elec connections on contactor are clean and tight but contactor does not pull in ?
aboilerfan
04-29-09, 07:43 AM
"OK to clarify, you get a good 24v from transformer to coil of contactor when there is a call for cooling, all elec connections on contactor are clean and tight but contactor does not pull in"
Exactly.
Exactly.
dun11
04-29-09, 07:55 AM
replace contactor, make sure you get one that has the correct FLA rating
aboilerfan
04-29-09, 08:25 AM
Since I did that originally, and it only solved the problem for a day and a half, I want to make sure there is not something else that could be causing the contactor to fail. I suppose it is possible I just got a bad contactor, but is there anything else I could/should look at?
dun11
04-29-09, 08:30 AM
You can chk incoming line voltage, also look to see if something is shorting out the coil on contactor.
Does the coil have continuity now ?
Does the coil have continuity now ?
aboilerfan
04-29-09, 09:24 AM
At work right now, so I can't recheck. But last night I was getting 240v on incoming line. After work I will recheck continuity and voltages.