Humidifiers and Dehumidifiers - Honeywell TrueIAQ wiring problem
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Honeywell TrueIAQ wiring problem
bdavis
04-20-09, 04:14 PM
Hello,
I've installed a Honeywell TrueIAQ, HE265DG115 by-pass, non-powered humidifier with Digital Control and a remote sensor. It does not work unless I change humidistat option 25-2, Hum forces fan on, or 25-3, Hum operates independent of fan. I believe that it should work when optioned to turn on when either heat or fan turns on Option 25-0,1. I've included a link to DigitalIAQ Qwners Guide which illustrates on page 11 how it should be wired.
I have a pretty good wiring schematic of the existing arrangement but am unable to include it with this msg. If anyone thinks it would help, I will gladly send it to an e-mail address. A picture is worth 1000 words, eh?
Any assistance is appreciated.
Thanks, Bdavis
http://www.ntsupply.com/files/products/69-2072.pdf
I've installed a Honeywell TrueIAQ, HE265DG115 by-pass, non-powered humidifier with Digital Control and a remote sensor. It does not work unless I change humidistat option 25-2, Hum forces fan on, or 25-3, Hum operates independent of fan. I believe that it should work when optioned to turn on when either heat or fan turns on Option 25-0,1. I've included a link to DigitalIAQ Qwners Guide which illustrates on page 11 how it should be wired.
I have a pretty good wiring schematic of the existing arrangement but am unable to include it with this msg. If anyone thinks it would help, I will gladly send it to an e-mail address. A picture is worth 1000 words, eh?
Any assistance is appreciated.
Thanks, Bdavis
http://www.ntsupply.com/files/products/69-2072.pdf
Jay11J
04-22-09, 08:07 PM
You may send the drawing to my e-mail
jaymarking at gmail dot com
jaymarking at gmail dot com
bdavis
04-29-09, 10:03 AM
Jay, Have you had the time to look at my wiring schematic? Any thoughts???
Thank You, BillD
Thank You, BillD
Jay11J
04-29-09, 11:47 AM
Yes, I did.. Did you get my reply?
The wire hooks up looks good, and was wondering what your settings are set to on the IAQ?
The wire hooks up looks good, and was wondering what your settings are set to on the IAQ?
bdavis
04-29-09, 12:53 PM
Jay,
IAQ Humidistat options: 10-1, 15-2, 20-55, 25-1, 30-0, 35 thru 40 not used, 45 thru 60 not used, 65-0, 80 thru 145 not used.
IAQ Humidistat options: 10-1, 15-2, 20-55, 25-1, 30-0, 35 thru 40 not used, 45 thru 60 not used, 65-0, 80 thru 145 not used.
Jay11J
04-29-09, 08:47 PM
All the settings are good.
So with 25 at 0, the humidfier is not coming on when there's call for heat?
So with 25 at 0, the humidfier is not coming on when there's call for heat?
bdavis
04-30-09, 01:12 PM
Jay,
Sorry about the delay in replying. We went to Home Depot and purchased about 800 sf of hardwood flooring for my next project.
With opt. 25 set to heat or fan (0 or 1), the humidifier does not turn on.
As of now, the only way that I'm able to engage the humidifier to turn on, is to use option 25-2 or 25-3.
Bill
Sorry about the delay in replying. We went to Home Depot and purchased about 800 sf of hardwood flooring for my next project.
With opt. 25 set to heat or fan (0 or 1), the humidifier does not turn on.
As of now, the only way that I'm able to engage the humidifier to turn on, is to use option 25-2 or 25-3.
Bill
Jay11J
05-02-09, 07:01 AM
Check to make sure you are getting power on IAQ's W from the t-stat. Also same for G.
Also double check the C wire at both spots.
Also double check the C wire at both spots.
bdavis
05-02-09, 02:04 PM
Jay,
Please give me a quick discription of what I am looking for on the w,g,r and c leads. Which is my return ground (C perhaps)?
All of the checking need be done at the heater with the t-stat operating I expect?
When no heat, no blower on, what should I read on the t-stat leads?
When burner on, what should I read on which t-stat leads
When burner and blower on, what should I read on the t-stat leads?
If you had a chance to look at my existing T-Stat wiring, only the Rc, Y and G are terminated on a common transformer.
The R and W are terminated on T1 and T2 of the burner control.
Thanks for your patience, Bill D.
Please give me a quick discription of what I am looking for on the w,g,r and c leads. Which is my return ground (C perhaps)?
All of the checking need be done at the heater with the t-stat operating I expect?
When no heat, no blower on, what should I read on the t-stat leads?
When burner on, what should I read on which t-stat leads
When burner and blower on, what should I read on the t-stat leads?
If you had a chance to look at my existing T-Stat wiring, only the Rc, Y and G are terminated on a common transformer.
The R and W are terminated on T1 and T2 of the burner control.
Thanks for your patience, Bill D.
Jay11J
05-07-09, 07:07 AM
Sorry for not getting back to you. I was on vacation, and got busy with other things around the house.
Jay,
Please give me a quick discription of what I am looking for on the w,g,r and c leads. Which is my return ground (C perhaps)?
R-C=24 volts.
Fan switch to on G-C=24 volts.
Fan switch to Auto (no call for cool) G-C= 0 volts
Call for heat W-C = 24 volts.
Call for cool Y-C = 24 volts.
All of the checking need be done at the heater with the t-stat operating I expect?
Correct
If you had a chance to look at my existing T-Stat wiring, only the Rc, Y and G are terminated on a common transformer.
The R and W are terminated on T1 and T2 of the burner control.
Yes, those are correct. There's no jumper between R and Rc right?
Jay,
Please give me a quick discription of what I am looking for on the w,g,r and c leads. Which is my return ground (C perhaps)?
R-C=24 volts.
Fan switch to on G-C=24 volts.
Fan switch to Auto (no call for cool) G-C= 0 volts
Call for heat W-C = 24 volts.
Call for cool Y-C = 24 volts.
All of the checking need be done at the heater with the t-stat operating I expect?
Correct
If you had a chance to look at my existing T-Stat wiring, only the Rc, Y and G are terminated on a common transformer.
The R and W are terminated on T1 and T2 of the burner control.
Yes, those are correct. There's no jumper between R and Rc right?
bdavis
05-11-09, 02:30 PM
Jay, Thank's for replying.
There is NO jumper between R&Rc.
I'll check those other voltages asap.
Bill D.
There is NO jumper between R&Rc.
I'll check those other voltages asap.
Bill D.
bdavis
05-12-09, 11:46 AM
Jay, I just checked voltages on those t-stat leads. R-C, 24v constant.... G-C, just as you indicated, 0v or 24v... W-C, 0v with heater on or off. The voltage never changes at the t-stat.
That would appear to be the reason that the humidistat control never turns on the humidifier.
Any thought of where I go from there?
Many thanks for the t-stat lead info. It gave me the info I needed to verify the t-stat control leads with reference to the(C) common lead.
Thanks, Bill D.
That would appear to be the reason that the humidistat control never turns on the humidifier.
Any thought of where I go from there?
Many thanks for the t-stat lead info. It gave me the info I needed to verify the t-stat control leads with reference to the(C) common lead.
Thanks, Bill D.
Jay11J
05-12-09, 02:26 PM
Ok, if you are not getting 24 volts on W on call of heat, then you have a break in the W line from the t-stat.
Check to make sure you have good connection from W at the t-stat down to W at the Humidifier.
Check to make sure you have good connection from W at the t-stat down to W at the Humidifier.
bdavis
05-13-09, 02:32 PM
Jay, It appears that I have a 2 transformer setup. The Honeywell t-stat has no jumper between R-Rc which indicates that it is a 2 transformer setup, which are isolated from each other....The Honeywell burner control that the t-stat R&W terminates on is supplying 24v, when the t-stat calls for heat it closes that circut. I verified that there is 24v at R-W on the t-stat with heat off. When heat comes on, the voltage drops to 0. If I make both 24v circuts common, won't I have 48v across all those 24v leads and propably blow everything on that circut?
Jay11J
05-13-09, 02:54 PM
I deleted the e-mail last night thinking I didn't need the drawing anymore.
Can you re send it again to me?
Thanks!
Can you re send it again to me?
Thanks!
wantonsoup
05-13-09, 07:10 PM
R-C=24 volts.
Fan switch to on G-C=24 volts.
Fan switch to Auto (no call for cool) G-C= 0 volts
Call for heat W-C = 24 volts.
Call for cool Y-C = 24 volts.
So - if you wanted to regulate the humidifier with the humidistat (and be able to run it during the spring/fall when you may not be calling for heat), could you wire the humidifier to G and C, and that would run it anytime the fan is on? (Hot, cold, or FAN ON mode). Is that correct thinking? I'm in Colorado and frankly we need humidification more than we need the furnace a lot of times.
Or - do I need to wire to R and C for the juice, and then use a current sensing relay on the "G" to turn it on?
As always - appreciate the help.
http://img8.imageshack.us/img8/3673/furnaceboard.th.jpg (http://img8.imageshack.us/img8/3673/furnaceboard.jpg)
Fan switch to on G-C=24 volts.
Fan switch to Auto (no call for cool) G-C= 0 volts
Call for heat W-C = 24 volts.
Call for cool Y-C = 24 volts.
So - if you wanted to regulate the humidifier with the humidistat (and be able to run it during the spring/fall when you may not be calling for heat), could you wire the humidifier to G and C, and that would run it anytime the fan is on? (Hot, cold, or FAN ON mode). Is that correct thinking? I'm in Colorado and frankly we need humidification more than we need the furnace a lot of times.
Or - do I need to wire to R and C for the juice, and then use a current sensing relay on the "G" to turn it on?
As always - appreciate the help.
http://img8.imageshack.us/img8/3673/furnaceboard.th.jpg (http://img8.imageshack.us/img8/3673/furnaceboard.jpg)
Jay11J
05-13-09, 08:23 PM
So - if you wanted to regulate the humidifier with the humidistat (and be able to run it during the spring/fall when you may not be calling for heat), could you wire the humidifier to G and C, and that would run it anytime the fan is on? (Hot, cold, or FAN ON mode). Is that correct thinking? I'm in Colorado and frankly we need humidification more than we need the furnace a lot of times.
You have the 700 Right? You could run it with the fan on, but honestly, lot of water is wasted down the drain.
You have the 700 Right? You could run it with the fan on, but honestly, lot of water is wasted down the drain.
wantonsoup
05-13-09, 08:26 PM
Yes - 700 with the simple manual humidistat. My thinking is that during the summer when I really don't want it on at all, I simply adjust the humidistat to off and it's done until I need it. Basically, we don't want to have to turn on the heat to get more humidity. It's been 80 degrees for 2 weeks but we're still at 22 percent relative humidity right now :(
What do you suggest for wiring? I'd love to avoid buying and installing the current sensing relay.
What do you suggest for wiring? I'd love to avoid buying and installing the current sensing relay.
Jay11J
05-13-09, 08:36 PM
Yes - 700 with the simple manual humidistat. My thinking is that during the summer when I really don't want it on at all, I simply adjust the humidistat to off and it's done until I need it. Basically, we don't want to have to turn on the heat to get more humidity. It's been 80 degrees for 2 weeks but we're still at 22 percent relative humidity right now :(
What do you suggest for wiring? I'd love to avoid buying and installing the current sensing relay.
What model Humidistat did you get?
I am afraid you may have to get the current sensing relay.
What do you suggest for wiring? I'd love to avoid buying and installing the current sensing relay.
What model Humidistat did you get?
I am afraid you may have to get the current sensing relay.
wantonsoup
05-13-09, 08:43 PM
It's their standard 2-wire manual one. Here's the wiring diagram they provide:
http://img22.imageshack.us/img22/8316/700mwiring.th.gif (http://img22.imageshack.us/img22/8316/700mwiring.gif)
http://img22.imageshack.us/img22/8316/700mwiring.th.gif (http://img22.imageshack.us/img22/8316/700mwiring.gif)
Jay11J
05-13-09, 09:35 PM
It's their standard 2-wire manual one. Here's the wiring diagram they provide:
Do you run your fan all times?
Do you run your fan all times?
wantonsoup
05-13-09, 11:07 PM
I'm becoming more and more convinced that the humidifier is defective.
1) The power fan on it runs continuously, whenever it's plugged in. Regardless of whether or not the 24v line is on or not. That can't be right...
2) The 24v line, when the circuit is closed, the voltage drops to 3v, the transformer gets super hot and starts to smell, and the water solenoid never opens.
I'm running out of ideas before I have to buy another one to swap for this unit.
1) The power fan on it runs continuously, whenever it's plugged in. Regardless of whether or not the 24v line is on or not. That can't be right...
2) The 24v line, when the circuit is closed, the voltage drops to 3v, the transformer gets super hot and starts to smell, and the water solenoid never opens.
I'm running out of ideas before I have to buy another one to swap for this unit.
bdavis
05-14-09, 10:24 AM
Jay, This may be a duplicate of a previously sent message. In any case, yes I have re-sent my schematic info to your e-mail
As always, Thanks.....Bill D.
As always, Thanks.....Bill D.
Jay11J
05-14-09, 04:36 PM
I'm becoming more and more convinced that the humidifier is defective.
1) The power fan on it runs continuously, whenever it's plugged in. Regardless of whether or not the 24v line is on or not. That can't be right...
2) The 24v line, when the circuit is closed, the voltage drops to 3v, the transformer gets super hot and starts to smell, and the water solenoid never opens.
I'm running out of ideas before I have to buy another one to swap for this unit.
With the humidistat wire taken off, it still runs?
if so, yeah something is wrong, and I'd contact the company you got this from and have it replaced under warranity.
1) The power fan on it runs continuously, whenever it's plugged in. Regardless of whether or not the 24v line is on or not. That can't be right...
2) The 24v line, when the circuit is closed, the voltage drops to 3v, the transformer gets super hot and starts to smell, and the water solenoid never opens.
I'm running out of ideas before I have to buy another one to swap for this unit.
With the humidistat wire taken off, it still runs?
if so, yeah something is wrong, and I'd contact the company you got this from and have it replaced under warranity.
Jay11J
05-14-09, 04:37 PM
Jay, This may be a duplicate of a previously sent message. In any case, yes I have re-sent my schematic info to your e-mail
As always, Thanks.....Bill D.
Got it, Thanks Bill.
What is the model # of the Honeywell Burner control?
As always, Thanks.....Bill D.
Got it, Thanks Bill.
What is the model # of the Honeywell Burner control?
bdavis
05-15-09, 03:15 PM
Jay, I have the orig. paperwork and was able to find the burner control and heater info. The Honeywell control closest resembles the R8184K model (no mfg. plate attached) and the heater is a Thermo Pride OH11. I scanned both wiring diag. and will send in a seperate e-mail.
Thanks, Bill D.
Thanks, Bill D.
Jay11J
05-19-09, 08:12 AM
Ok, looks like we are going to need add a relay between the burner control and the IAQ.
Remove the W wire before we do any damage to anything.
Will need to add a relay like #94-390.
Remove the W wire before we do any damage to anything.
Will need to add a relay like #94-390.
bdavis
05-19-09, 12:32 PM
Jay, OK with the relay. Would it be the same as Aprilaire 24v
Current Sensing relay? I'll order whichever if you can get back to me before the end of the day. I'll be in Minneapolis Wed. thru Mon. next week, and be out of touch. I understand why you want to remove the white wire from the humidistat. Also, if you have relay wiring directions available all the better.
As always, Thank You, Bill D.
Current Sensing relay? I'll order whichever if you can get back to me before the end of the day. I'll be in Minneapolis Wed. thru Mon. next week, and be out of touch. I understand why you want to remove the white wire from the humidistat. Also, if you have relay wiring directions available all the better.
As always, Thank You, Bill D.
Jay11J
05-19-09, 03:12 PM
Any relay with 120 volt coil will work.
It can be found on E-Bay (http://cgi.ebay.com/NIB-Furnace-Relay--110-120-volt-coil-2NO%2f2NC-Contacts-_W0QQitemZ370118801085QQcmdZViewItem).
You won't be to far from me when you are in Mpls. It's 90˚ out right now.
It can be found on E-Bay (http://cgi.ebay.com/NIB-Furnace-Relay--110-120-volt-coil-2NO%2f2NC-Contacts-_W0QQitemZ370118801085QQcmdZViewItem).
You won't be to far from me when you are in Mpls. It's 90˚ out right now.