Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Pc 5132 rs
Danigo
03-15-09, 04:15 PM
Hi,
I bought a house with DSC PC 5010 installed with LED control pnl, door sensor, two wired motion sensors and PC 5132 RS rec. with two WLS 904 motion sensors. Previous owner did not leave me any codes so I downloaded the manuals (Installer, Program and Remote control) and I managed to program all zones, sensors, delays etc. I have only problem with "Enable Supervision" Chapter 2.8 Section [902] and [903]. The system does not confirm PC5132RS as being connected to the system as per [903]. I checked all connections, power etc. and all seems in place as per manual.
When I do the check [903] it lites up zone lite "1" only(=Keypad 1 present) but when I try to advance to next # by pressing emergency key it beeps short and long, but no other #'s will lite up (it should lite up #9 for zones 9to12 present and #17 for PC5132 present).
And yet when I do 2.6 "Testing W/less Devices/Module Placement Test" section [904], the system Beeps/Squawks for both w/less sensors as it supposed to.
Also when the system is armed all sensors cause the alarm as expected (delays, bypass etc.) except those two W/less sensors. What am I missing??
Danigo
I bought a house with DSC PC 5010 installed with LED control pnl, door sensor, two wired motion sensors and PC 5132 RS rec. with two WLS 904 motion sensors. Previous owner did not leave me any codes so I downloaded the manuals (Installer, Program and Remote control) and I managed to program all zones, sensors, delays etc. I have only problem with "Enable Supervision" Chapter 2.8 Section [902] and [903]. The system does not confirm PC5132RS as being connected to the system as per [903]. I checked all connections, power etc. and all seems in place as per manual.
When I do the check [903] it lites up zone lite "1" only(=Keypad 1 present) but when I try to advance to next # by pressing emergency key it beeps short and long, but no other #'s will lite up (it should lite up #9 for zones 9to12 present and #17 for PC5132 present).
And yet when I do 2.6 "Testing W/less Devices/Module Placement Test" section [904], the system Beeps/Squawks for both w/less sensors as it supposed to.
Also when the system is armed all sensors cause the alarm as expected (delays, bypass etc.) except those two W/less sensors. What am I missing??
Danigo
LOCKtec
03-15-09, 05:35 PM
assume all is on partition 1
did you do section 202? for each zone LED lit- these are zones that are enabled (report to the panel)
LED's 1-8 in section 202 is for zones 1-8, LED's 1-8 in section 203 is for zones 9 - 16, etc.
only LED's 1-8 are used. (if your keypad is a 16 or 32 zone model, the additional LED's are NOT used)
what zones are you putting the wireless PIR's on?
you can not put anything on zones 9 & up if there are NO zone expander boards installed.
What is meant by advancing using the emergency key?
When you do a 903 the zone LED's 1-24 tell ALL that is there- no advance is required.
How about a 902 reset? then a 903?
Are using a 8 zone keypad- you will not see what modules are installed, only Keypad #1. 1-8 are telling what keypads are present.
If your not using 8 zones, assign the 2 wireless zones to zones 7 & 8. You can not mix wireless & wired zones on the same input zone.
did you do section 202? for each zone LED lit- these are zones that are enabled (report to the panel)
LED's 1-8 in section 202 is for zones 1-8, LED's 1-8 in section 203 is for zones 9 - 16, etc.
only LED's 1-8 are used. (if your keypad is a 16 or 32 zone model, the additional LED's are NOT used)
what zones are you putting the wireless PIR's on?
you can not put anything on zones 9 & up if there are NO zone expander boards installed.
What is meant by advancing using the emergency key?
When you do a 903 the zone LED's 1-24 tell ALL that is there- no advance is required.
How about a 902 reset? then a 903?
Are using a 8 zone keypad- you will not see what modules are installed, only Keypad #1. 1-8 are telling what keypads are present.
If your not using 8 zones, assign the 2 wireless zones to zones 7 & 8. You can not mix wireless & wired zones on the same input zone.