Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




wankel7
02-23-09, 12:47 PM
I just moved into a home that has a Amana 95% furnace. And it also has a solar hot water system. The solar system has a heat exchanger that is in front of the furnace air inlet.

It looks like the water pump that moves the water there was only to be operating when the furnace blower was on.

The issue was when the company that installed the furnace installed it. They just put the junction box on the furnace. They didn't hook up the power wires for the system or the furnace h20 pump.

So , the solar has four wires coming from it. Red (Marked power), black (Marked blower), white, and bare copper ground.

So, I assume I will hook up the Red, White, and copper to a 120v source to get power to the other pumps?

My question:

The blower wire (Black). I have been reading the instruction manual for the furnace and it shows it has an accessory output. EAC and can handle 1 amp 120V. The water pump says 0.63 amps at 120V. So, I guess the furnace board can handle this.

Do I simply connect the Blower wire from the solar pump to this EAC output on the furnace board?

That is the way it looks on the diagram. But I was confused by the " line neutral. What would that wire be?

Thank you !

http://img.photobucket.com/albums/v238/rotaryr/amana.jpg


cyberdead
02-23-09, 08:10 PM
you could just add a 24v relay wired to w and common to energize the rely making the contacts to power the pump.. you dont want the pump running when the blower is running in ac mode..
the other option is to use the humid option and wire to the blower heat speed.

wankel7
02-23-09, 08:26 PM
you could just add a 24v relay wired to w and common to energize the rely making the contacts to power the pump.. you dont want the pump running when the blower is running in ac mode..
the other option is to use the humid option and wire to the blower heat speed.

I am running just a heating system...with a swamp cooler for cooling.

So, it would be ok to use the EAC control?


cyberdead
02-23-09, 09:10 PM
personally I would put a relay between your pump and the board.
to make certain that I did not overload the boar. Small price to pay. OR better yet add a current sensing relay to the motor wires. As used for a HUMID.