Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Bryant Series 90 / Truesteam / IAQ
Buckeyeboy
02-19-09, 07:05 PM
View HTML | Text | Header | Raw Content
Hi,
I have a VisionPro IAQ w/ EIM and a 12 gallon TrueSteam that I will be installing.
The furnace is a Bryant Model # 350AAV
The A/C is a Bryant model # 113a/114a
New Home, Central Ohio, 3800 SQ ft. 5 level split (looks like 2 story from outside), completed Sept. 2007
As far as I can tell, I would wire the EIM and Furnace this way:
EIM ---- Furnace
C ---- COM 24V
R* ----- R
W1 ----- W
Y ----- Y/Y2
G ---- G
* (factory installed jumpers on EIM at R/RC/RH)
Can I leave the two wires that control the A/C unit connected to the Furnace Relay board or should I move those to the EIM?
If I were to the move the A/C wires to the EIM, would this be correct:
EIM --------- A/C unit outside
C --------- White wire to A/C outside
Y --------- Red wire to A/C outside
Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:
EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace
I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
(I will also set DIP 4 ON (no AFS) all other DIP switches OFF)
As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?
I will then wire the outdoor thermometer this way:
EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor
I will then set the following installer options:
100 – 0 Not Zoned
172 – 1 Conventional
180 – 0 Gas / Oil Furnace controls fan in heating
280 – 1 Backlight on
300 – 1 Auto Change over for those cold mornings (20’s)and warm afternoons (80’s)
330 - 2 DST (US 2007)
342 – 1 Outdoor temp sensor
370 - 1 Internal Sensor in Thermostat
372 – 3 Humidity with Frost protection (Frost setting 5 at VisionPro)
374 – 1 Humidity will Force Fan on
379 – 1 Dehumidify with Air Conditioning
383 – 3 Over cooling limit 1.5
500 – 4 90 runtime days
Thank you for checking my work, I do appreciate it.
Hi,
I have a VisionPro IAQ w/ EIM and a 12 gallon TrueSteam that I will be installing.
The furnace is a Bryant Model # 350AAV
The A/C is a Bryant model # 113a/114a
New Home, Central Ohio, 3800 SQ ft. 5 level split (looks like 2 story from outside), completed Sept. 2007
As far as I can tell, I would wire the EIM and Furnace this way:
EIM ---- Furnace
C ---- COM 24V
R* ----- R
W1 ----- W
Y ----- Y/Y2
G ---- G
* (factory installed jumpers on EIM at R/RC/RH)
Can I leave the two wires that control the A/C unit connected to the Furnace Relay board or should I move those to the EIM?
If I were to the move the A/C wires to the EIM, would this be correct:
EIM --------- A/C unit outside
C --------- White wire to A/C outside
Y --------- Red wire to A/C outside
Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:
EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace
I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
(I will also set DIP 4 ON (no AFS) all other DIP switches OFF)
As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?
I will then wire the outdoor thermometer this way:
EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor
I will then set the following installer options:
100 – 0 Not Zoned
172 – 1 Conventional
180 – 0 Gas / Oil Furnace controls fan in heating
280 – 1 Backlight on
300 – 1 Auto Change over for those cold mornings (20’s)and warm afternoons (80’s)
330 - 2 DST (US 2007)
342 – 1 Outdoor temp sensor
370 - 1 Internal Sensor in Thermostat
372 – 3 Humidity with Frost protection (Frost setting 5 at VisionPro)
374 – 1 Humidity will Force Fan on
379 – 1 Dehumidify with Air Conditioning
383 – 3 Over cooling limit 1.5
500 – 4 90 runtime days
Thank you for checking my work, I do appreciate it.
Jay11J
02-19-09, 07:53 PM
Can I leave the two wires that control the A/C unit connected to the Furnace Relay board or should I move those to the EIM?
Yes, you can leave those on the furnace.
Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:
EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace
Correct.
I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
Correct.
As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?
False. Steam works well with warm or cold air. The flow though type unit don't work well with room air temps.
I will then wire the outdoor thermometer this way:
EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor
Correct.
I will then set the following installer options:
Looks good. And anything with "E" shown on the screen change it to a number value.
Set the CPH to 3 for both heat and cool.
Yes, you can leave those on the furnace.
Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:
EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace
Correct.
I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
Correct.
As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?
False. Steam works well with warm or cold air. The flow though type unit don't work well with room air temps.
I will then wire the outdoor thermometer this way:
EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor
Correct.
I will then set the following installer options:
Looks good. And anything with "E" shown on the screen change it to a number value.
Set the CPH to 3 for both heat and cool.
Buckeyeboy
02-20-09, 06:14 AM
Set the CPH to 3 for both heat and cool.
I do not seem to be able to set the following:
220 - 3 CPH Cool
240 - 3 CPH Heat
I DO NOT have a Heat Pump, is that why?
I do not seem to be able to set the following:
220 - 3 CPH Cool
240 - 3 CPH Heat
I DO NOT have a Heat Pump, is that why?
Jay11J
02-20-09, 06:27 AM
220, and 240 should show up on the screen... Are you in the advance installer set up menu, or home owener set up?
Buckeyeboy
02-20-09, 07:32 AM
D'oh!!:Homer:
I would be now...
User setup =
Press System Key,
Press and Hold Center Blank Key for 5 seconds
Installer Setup =
Press System Key,
Press and hold the two keys on EITHER side of the Center Key for 5 seconds
I would be now...
User setup =
Press System Key,
Press and Hold Center Blank Key for 5 seconds
Installer Setup =
Press System Key,
Press and hold the two keys on EITHER side of the Center Key for 5 seconds
Jay11J
02-20-09, 04:48 PM
:-)
Good Pix of Homer.. Did you get it all up and running now?
Good Pix of Homer.. Did you get it all up and running now?
Buckeyeboy
02-22-09, 05:19 AM
Yes, all systems up and running.
Thanks for the help...
Thanks for the help...
Jay11J
02-22-09, 07:22 AM
Thanks for the update, and glad to see it's up and running.