Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




Buckeyeboy
02-19-09, 07:05 PM
View HTML | Text | Header | Raw Content


Hi,



I have a VisionPro IAQ w/ EIM and a 12 gallon TrueSteam that I will be installing.

The furnace is a Bryant Model # 350AAV

The A/C is a Bryant model # 113a/114a

New Home, Central Ohio, 3800 SQ ft. 5 level split (looks like 2 story from outside), completed Sept. 2007

As far as I can tell, I would wire the EIM and Furnace this way:

EIM ---- Furnace
C ---- COM 24V
R* ----- R
W1 ----- W
Y ----- Y/Y2
G ---- G

* (factory installed jumpers on EIM at R/RC/RH)

Can I leave the two wires that control the A/C unit connected to the Furnace Relay board or should I move those to the EIM?

If I were to the move the A/C wires to the EIM, would this be correct:

EIM --------- A/C unit outside
C --------- White wire to A/C outside
Y --------- Red wire to A/C outside

Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:

EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace

I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
(I will also set DIP 4 ON (no AFS) all other DIP switches OFF)

As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?

I will then wire the outdoor thermometer this way:

EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor

I will then set the following installer options:

100 – 0 Not Zoned
172 – 1 Conventional
180 – 0 Gas / Oil Furnace controls fan in heating
280 – 1 Backlight on
300 – 1 Auto Change over for those cold mornings (20’s)and warm afternoons (80’s)
330 - 2 DST (US 2007)
342 – 1 Outdoor temp sensor
370 - 1 Internal Sensor in Thermostat
372 – 3 Humidity with Frost protection (Frost setting 5 at VisionPro)
374 – 1 Humidity will Force Fan on
379 – 1 Dehumidify with Air Conditioning
383 – 3 Over cooling limit 1.5
500 – 4 90 runtime days

Thank you for checking my work, I do appreciate it.


Jay11J
02-19-09, 07:53 PM
Can I leave the two wires that control the A/C unit connected to the Furnace Relay board or should I move those to the EIM?
Yes, you can leave those on the furnace.


Is it possible to use my furnace for dehumidifying? If so, would this be the correct wiring:

EIM ------- Add jumper from R/RC/RH to DHM1 (lower left on EIM)
DHM2 ------- DHUM on furnace
Correct.

I will then add the TrueSteam as follows:
EIM -------- TrueSteam
Hum1 -------- Hum
Hum2 -------- Hum
Correct.



As I understand it, having the TrueSteam wired for independent fan contol is a bad idea. Humidification via cold air (blower only) is inefficient. T or F?
False. Steam works well with warm or cold air. The flow though type unit don't work well with room air temps.

I will then wire the outdoor thermometer this way:

EIM --------- Outdoor Thermometer
Out 1 --------- wire from sensor
Out 2 --------- wire from sensor
Correct.

I will then set the following installer options:

Looks good. And anything with "E" shown on the screen change it to a number value.

Set the CPH to 3 for both heat and cool.

Buckeyeboy
02-20-09, 06:14 AM
Set the CPH to 3 for both heat and cool.

I do not seem to be able to set the following:

220 - 3 CPH Cool
240 - 3 CPH Heat

I DO NOT have a Heat Pump, is that why?


Jay11J
02-20-09, 06:27 AM
220, and 240 should show up on the screen... Are you in the advance installer set up menu, or home owener set up?

Buckeyeboy
02-20-09, 07:32 AM
D'oh!!:Homer:

I would be now...

User setup =
Press System Key,
Press and Hold Center Blank Key for 5 seconds

Installer Setup =
Press System Key,
Press and hold the two keys on EITHER side of the Center Key for 5 seconds

Jay11J
02-20-09, 04:48 PM
:-)

Good Pix of Homer.. Did you get it all up and running now?

Buckeyeboy
02-22-09, 05:19 AM
Yes, all systems up and running.

Thanks for the help...