Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Attaching Aprilaire 700 to Rheem furnace
mancillaj
02-17-09, 08:36 AM
I have a Rheem furnace would like to connect my Aprilaire 700 humidifier with automatic humidifier control, to.
I have checked and the connections on the left of the furnace circuit box, they are 24V, which are hot all the time.
The connections are labeled as: Y, G, W, R, C
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture002.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture004.jpg
One problem I am having is, the automatic control I have does not match the diagram I received. The control has 6 connections, two labeled – 24V, two labeled – A/A, and the last two are for the outside temperature sensor, which I have figured out.
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture007.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture008.jpg
Have no idea what the A/A connections are for.
The Aprilaire 700 system has the solenoid attached to the same 110V that the fan is.
Then there are the two brown wires where are also attached to the plug as the solenoid.
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture001.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture.jpg
The furnace is a Rheem model# RGED-06EMAES
I have checked and the connections on the left of the furnace circuit box, they are 24V, which are hot all the time.
The connections are labeled as: Y, G, W, R, C
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture002.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture004.jpg
One problem I am having is, the automatic control I have does not match the diagram I received. The control has 6 connections, two labeled – 24V, two labeled – A/A, and the last two are for the outside temperature sensor, which I have figured out.
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture007.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture008.jpg
Have no idea what the A/A connections are for.
The Aprilaire 700 system has the solenoid attached to the same 110V that the fan is.
Then there are the two brown wires where are also attached to the plug as the solenoid.
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture001.jpg
http://i598.photobucket.com/albums/tt63/titoandscuba/Picture.jpg
The furnace is a Rheem model# RGED-06EMAES
Jay11J
02-17-09, 09:12 AM
That's an old humidistat.. Are you reusing this or was this already there?
I can't find the manual for this humidistat, R and C on the furnace will be your power, from there I am blind.
If you got the manual, scan or photo it for me to see.
I can't find the manual for this humidistat, R and C on the furnace will be your power, from there I am blind.
If you got the manual, scan or photo it for me to see.
mancillaj
02-17-09, 07:34 PM
The manual I have is not for this humidistat, looks totally different.
I purchased it from this guy, appeared brand new in the box.
I purchased it from this guy, appeared brand new in the box.
Jay11J
02-17-09, 09:53 PM
Ok.. I tired finding the manual for that's year model ('02) and I can't find anything.
Do you have a multi meter?
Do you have a multi meter?
mancillaj
02-18-09, 07:09 AM
Yes, I do have a multi meter.
Jay11J
02-18-09, 12:26 PM
Put it on OHM scale, and take a reading between the two "output" and see if that open and close as you change the dial.
If nothing, then try between Output, and one of 24v section.
If nothing, then try between Output, and one of 24v section.
mancillaj
02-20-09, 08:22 AM
Jay11J,
Thanks for all your help with this.
I contacted AprilAire and they were able to email me a PDF of the correct manual. They called it the "old model" 56.
If you would like me to send it your way, just let me know.
Thanks again for you support.
Did all this work, didn't want it to go to waste.
With humidity control in Off or Test position, temperature sensor shorted and un-shorted, results did not change. Pins 1 thru 5 not shorted.
(Pins: 1-Bottom / 5-Top )
Pin 1 connects with 24v Left
Pin 2 is dead
Pin 3 connects with Output Left
Pin 4 connects with 24v Right
Pin 5 is dead
With Pins 1 & 2 shorted along with 4 & 5 shorted – No change with or without temperature shorted or humidity control in Off or Test position.
With Pins 1 & 2 shorted along with 3 & 4 shorted – 24v Right & Output Left connected.
No change with or without temperature shorted or humidity control in Off or Test position.
No other connections found.
Hope this helps and doesn’t give too much information.
I too have been searching for any information on this control board.
Thanks for all your help with this.
I contacted AprilAire and they were able to email me a PDF of the correct manual. They called it the "old model" 56.
If you would like me to send it your way, just let me know.
Thanks again for you support.
Did all this work, didn't want it to go to waste.
With humidity control in Off or Test position, temperature sensor shorted and un-shorted, results did not change. Pins 1 thru 5 not shorted.
(Pins: 1-Bottom / 5-Top )
Pin 1 connects with 24v Left
Pin 2 is dead
Pin 3 connects with Output Left
Pin 4 connects with 24v Right
Pin 5 is dead
With Pins 1 & 2 shorted along with 4 & 5 shorted – No change with or without temperature shorted or humidity control in Off or Test position.
With Pins 1 & 2 shorted along with 3 & 4 shorted – 24v Right & Output Left connected.
No change with or without temperature shorted or humidity control in Off or Test position.
No other connections found.
Hope this helps and doesn’t give too much information.
I too have been searching for any information on this control board.
Jay11J
02-20-09, 04:47 PM
Yeah, could you please send that manual over to me?
jaymarking at gmail dot com
jaymarking at gmail dot com
Jay11J
02-20-09, 08:15 PM
ok, Tie the 24 v to R and C on the furnace.
Then the Output to the two brown humidifier wires.
Then the Output to the two brown humidifier wires.
Jay11J
02-20-09, 08:25 PM
My Bad.. I mean W and C.... NOT R and C.. My mind was thinking of the newer style t-stat.
mancillaj
02-21-09, 06:56 AM
Thanks for the update. I did try the R & C....it would run all the time. When I checked, the W & C would only have power when the furnace did.
Thanks again for all your help...
Thanks again for all your help...