Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : #of lights per run of track lights
Dayton
02-14-09, 06:40 PM
How do I calculate the number of light fixtures a 12 ft. run of track lights will handle? The light fixture I like uses 50 watt bulbs. Is there voltage use of the fixture itself? I've tried playing with the formula W=V.A but the numbers I come up with don't seem realistic. (help, math was 35 years ago). :wall:
HotinOKC
02-14-09, 07:22 PM
The track systems should have given you a limit? No?
I would say (6) lamps, so that would be 300W.
A 20amp circuit can handle 2400w's. 15 amp circuit can handle 1800w
I would say (6) lamps, so that would be 300W.
A 20amp circuit can handle 2400w's. 15 amp circuit can handle 1800w
Dayton
02-14-09, 07:56 PM
Thanks for the reply. That is what I came up with. I read in an article not to overload the circuit but they said not to go over 20 amps which would be a lot of lamps. I'll check with the supplier to be sure.
HotinOKC
02-15-09, 06:21 AM
The light won't overload the circuit alone, you just have to know what else shares that circuit with it.....
Rick Johnston
02-15-09, 02:13 PM
A 12-foot track would have to hold forty-eight 50-watt lights to draw 20 amps at 120 volts.
For pure resistive loads like light bulbs, the formula is P=I*E
P = power (watts)
I = current (amps)
E = voltage
Put another way: I = P/E
It's never a good idea to fully load a circuit, though. Also many residential lighting circuits are 15 amps, not 20. 15 amps = thirty-six 50-watt lamps.
You are talking about 120-volt lamps, right? Not a low-voltage track with a transformer? In that case, the transformer dictates the maximum cumulative wattage of the lamps on the track. It's a good idea to leave 20% headroom on a power transformer. (Example, four 20-watt lamps on a 100-watt transformer.)
For pure resistive loads like light bulbs, the formula is P=I*E
P = power (watts)
I = current (amps)
E = voltage
Put another way: I = P/E
It's never a good idea to fully load a circuit, though. Also many residential lighting circuits are 15 amps, not 20. 15 amps = thirty-six 50-watt lamps.
You are talking about 120-volt lamps, right? Not a low-voltage track with a transformer? In that case, the transformer dictates the maximum cumulative wattage of the lamps on the track. It's a good idea to leave 20% headroom on a power transformer. (Example, four 20-watt lamps on a 100-watt transformer.)