Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : DSC Power 832 and Smoke Detectors
JMRoux
12-24-08, 09:50 AM
I have a DSC Power 832 system and had to reprogram the system. I had no problem with the alarm portion of the system, but I'm having difficulty with the smoke detectors. the smoke detectors are System Sensors model 2100TS. I have two detectors...one in the kitchen and another in a hallway, the one in the kitchen was removed due to work in that room. The kitchen unit has 2 sets of wires coming into it. I'm assumming one set of wires to the control box and the other to the detector in the hallway (note: the detector in the hallway only has 1 set and a resistor at the end). the wire in the control box is wired for a two wire set...red to Aux+ and black to Prg2. The detector has 5 connectors +,+,-, +led, -led. Question, how do I wire the the smoke detector (which terminals) and second, how do I program the panel to recognize the smoke detectors (note: I have the installers code as I had to reprogram the system)
Thanks in advance
Thanks in advance
MrRonFL
12-24-08, 12:48 PM
First, fix your wiring. The resistor must be 2.2k ohm (3 red stripes for the first 3 bands). One leg of the resistor goes on either + terminal (it doesn't matter which). The other leg goes to - with the black wire. The red wire goes on the unused + terminal. The led terminals are not used (in this configuration).
The programming (and no, DSC doesn't make two wire smoke configuration easy):
2 wire smokes must connect to PGM 2, which should be correct if all you did was default the panel.
Assuming that there is currently nothing on PGM1:
Go to program *8 [installer code]
009 19 04
Exit programming.
The programming (and no, DSC doesn't make two wire smoke configuration easy):
2 wire smokes must connect to PGM 2, which should be correct if all you did was default the panel.
Assuming that there is currently nothing on PGM1:
Go to program *8 [installer code]
009 19 04
Exit programming.
JMRoux
12-24-08, 02:06 PM
Thank you for the programming code....sorry I wasn't correct on my description of the wiring...when I referred to one set of wiring at the back detector, I was stating that the was one 2-wire cable coming in with a 2.2 ohm resistor between the red and black lead...
The programming code corrected the issue...Thanks for a great site and quick response
The programming code corrected the issue...Thanks for a great site and quick response
MrRonFL
12-24-08, 02:27 PM
The way you had it will _function_. The way I described is the correct wiring. The intent is to produce a system trouble if the connector is removed from the back of the smoke (it's the manufacturers instructions... and nfpa 72 code (fire alarm code)).