Humidifiers and Dehumidifiers - Aprilaire 600A Humidity Too Low

Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Aprilaire 600A Humidity Too Low


jsbigger
12-04-08, 11:15 AM
Last spring I installed an Aprilaire 600A bypass humidifier to replace a much older Aprilaire unit.

I live in MN, and only able to get the humidity to 30%...I would like 35-40%

We live in a two story walk about home with about 3000 sq feet of space.

The water line is connected to hot water. I have set my Honewell IAQ thermostat to run the fan continuously, and the humdifier runs while the fan is on.

I have noticed that the water flow to the pan at the top of the humdifier is much slower than my old unit. When I hold the pan level, the water drips out of each hole at about one drip per second. I have checked the saddle valve and it is wide open.

I am wondering if the issue here is that the water flow is less than that it should be? How do I determine that?

What else should I check?

Thanks!


Jay11J
12-04-08, 08:13 PM
Have you removed the screen on the valve to see if it's clean?

Sounds like the screen is plugged.

While you got the water line unhooked, put the line into a bucket, and open the valve to flush out the line, it should blow pretty hard.

Do you have an outdoor sensor on your IAQ, and frost guard on or off?

TheCaptain
12-04-08, 09:02 PM
I assume you have adjusted the humidstat to a higher setting? Mine is set to 4 and I have only a 1500 Sq house with what would be called "leaky". ---Old house.

Is this on manual or automatic control when you wired it up?

I have the same model and installed it about a month ago.

Also, you can plumb it to hot water for maximum evaporation if needed, but I cannot imagine you would get that much more out of hot water...


jsbigger
12-06-08, 01:42 PM
I assume you have adjusted the humidstat to a higher setting? Mine is set to 4 and I have only a 1500 Sq house with what would be called "leaky". ---Old house.

Is this on manual or automatic control when you wired it up?

I have the same model and installed it about a month ago.

Also, you can plumb it to hot water for maximum evaporation if needed, but I cannot imagine you would get that much more out of hot water...

I have my Honeywell IAQ humidity set to 38, but actual is only 28. I wired the humdifier to the IAQ control

It is connected to hot water

Thanks

jsbigger
12-06-08, 02:01 PM
Have you removed the screen on the valve to see if it's clean?

Sounds like the screen is plugged.

While you got the water line unhooked, put the line into a bucket, and open the valve to flush out the line, it should blow pretty hard.

Do you have an outdoor sensor on your IAQ, and frost guard on or off?

Hi Jay, I removed the water line and solenoid. There was a plastic plug in the end of the platic line that runs from the solenoid to the humidifier...is this the screen? It looks OK.

Water pressure is strong thru the copper water line to the solenoid. I disconnected the plastic water line between the solenoid and the humdifier. I then tested water flow thru the solenoid with the solenoid open, and closed.

When open, the water that goes thru the solenoid is just a trickle...so something is restricting the water flow. When closed, the water stops.

I was wondering if the solenoid might not have enough current to open all the way. My volt meter is over at my daughters house right now.

I wired this per page 1 of the wiring guide for the Honeywell Vision Pro IAQ. I used the "without power supply" wiring guide. One wire from the solenoid is connected to the common terminal on the IAQ, and the other wire is connected to the M2 terminal. Per the diagram, H1 is jumpered to RH, and RH, and RH is connected to RC and R. Please let me know if this is correct.

It would seem that there is clogged screen that I can not locate, or there is problem with the wiring that causes the solenoid to only party open, or the solenoid is defective. Keep in mind this humidifier is less than a year old.

I do not have an outdoor humidity sensor, and frost guard is off.


What do you think?

Thanks much!



Jeff

Puchatek
12-06-08, 02:34 PM
I'm also having performance problems with my Aprilaire 600A humidifier. I seem to be having a good water-flow, but for some reason the insert is not pulling the water up from the pan. I just installed a new insert 2 months ago, and from the beginning I could see that the insert only gets 1/3 moist (bottom 1/3), now it doesn't seem to be pulling any water at all. My theory is that calcium deposits are interfering with the wicking action and after couple of weeks the insert is useless. I'm considering modding my 600A and installing a small circulating pump that would get the water from the pan and continuously spray it to the top of the insert. :thinker: Any thoughts on this idea? Oh, my house humidity is at 31% - stat set to 50%.

--Rob in VA

jsbigger
12-06-08, 03:29 PM
I'm also having performance problems with my Aprilaire 600A humidifier. I seem to be having a good water-flow, but for some reason the insert is not pulling the water up from the pan. I just installed a new insert 2 months ago, and from the beginning I could see that the insert only gets 1/3 moist (bottom 1/3), now it doesn't seem to be pulling any water at all. My theory is that calcium deposits are interfering with the wicking action and after couple of weeks the insert is useless. I'm considering modding my 600A and installing a small circulating pump that would get the water from the pan and continuously spray it to the top of the insert. :thinker: Any thoughts on this idea? Oh, my house humidity is at 31% - stat set to 50%.

--Rob in VA

Rob, How fast does the water discharge from your unit? With mine is is a fast drip or a very slow trickle. That does not seem right to me. Per below, I think I probably have a bad solenoid.

Jay11J
12-06-08, 04:46 PM
is this the screen? It looks OK.
Yes.


When open, the water that goes thru the solenoid is just a trickle...so something is restricting the water flow. When closed, the water stops.
Undo the line again, remove screen, then turn on the solenoid, and blow into the hose that the water goes into the pad.. (Blow back out where the water would come in..)


I was wondering if the solenoid might not have enough current to open all the way. My volt meter is over at my daughters house right now.
Maybe?? it's either open or closed... Could try to see what your voltage is.


I wired this per page 1 of the wiring guide for the Honeywell Vision Pro IAQ. I used the "without power supply" wiring guide. One wire from the solenoid is connected to the common terminal on the IAQ, and the other wire is connected to the M2 terminal. Per the diagram, H1 is jumpered to RH, and RH, and RH is connected to RC and R. Please let me know if this is correct.
Yep, that is correct.

Jay11J
12-06-08, 04:48 PM
for some reason the insert is not pulling the water up from the pan.
Do you have the metal type pad or the paper type? These style of unit don't pull the water up.. They are the "Flow though" type. Water flows from the top down to the bottom and out the drain.

Is the water in the top tray going across the whole thing even, and also is the tray coated in this "Sand" like products?

Jay11J
12-06-08, 04:50 PM
Rob, How fast does the water discharge from your unit? With mine is is a fast drip or a very slow trickle. That does not seem right to me. Per below, I think I probably have a bad solenoid.

Should be a steady stream... About 1/4" stream..

jsbigger
12-06-08, 05:50 PM
Jay, I tried blowing into the open solenoid (oppositie direction of water flow) and the air did not move very fast. Then I hooked up the water line again, and the water flow continues thru the solenoid continues to flow at a fast drip at best.

Absent any problem with voltage, should I get a new solednoid?

Thanks!

Jeff

Jay11J
12-06-08, 06:44 PM
Have you undone the line from the "outlet" side of the valve, and blow into that?

if that blows free, then you may have a bad valve.

jsbigger
12-06-08, 08:55 PM
Jay, I blew into the outlet side of the valve when the valve was open. I was able to blow air thru it.....

Jeff

Jay11J
12-06-08, 09:13 PM
Now blow in the hose that feeds the top tray.

Jay11J
12-06-08, 09:22 PM
Also, what color is the orifice?

jsbigger
12-06-08, 10:24 PM
Jay, the ofirice is yellow. When I blow in the hose that feeds the top tray without the orifice in the hose, it is easy to blow air. With the orifice in the hose, it is difficult.

Jeff

Jay11J
12-06-08, 10:28 PM
Ok, the yellow one is correct one.

The opening is a small hole, and make sure that is clear.

I am off to bed. Good night.

jsbigger
12-07-08, 06:56 AM
Jay, as I previously mentioned, when I disconnect the plastic water line between the valve and the top of the humidifer, the flow of water is only a faster drip when the valve is open. Should the flow be faster than this out of the valve?

TheCaptain
12-07-08, 08:39 AM
Jay, as I previously mentioned, when I disconnect the plastic water line between the valve and the top of the humidifer, the flow of water is only a faster drip when the valve is open. Should the flow be faster than this out of the valve?

You mean straight off the water source, through your saddle or whatever you used... and out of a water line direct? That could depend on your inside plumbing, but it should be more like a sink running kind of slowly, depending on the size of your plastic tube you mentioned.

Rather than a drip, it should be a flow of water. Check your tap or water source to make sure its not partly closed.

Or rather, take a picture of this water tap so we can see.

Do you use well-water or city water?

Puchatek
12-07-08, 10:02 AM
Do you have the metal type pad or the paper type? These style of unit don't pull the water up.. They are the "Flow though" type. Water flows from the top down to the bottom and out the drain.

Is the water in the top tray going across the whole thing even, and also is the tray coated in this "Sand" like products?

I have a combination metal/paper pad that is supposed to wick the water up. While there is a drain on the unit, this model is not supposed to be continuously flowing and draining. The pan fills up and there are two floating cut-off switches that shut-off the solenoid when the pan is full of water.

Jay11J
12-07-08, 11:44 AM
I have a combination metal/paper pad that is supposed to wick the water up. While there is a drain on the unit, this model is not supposed to be continuously flowing and draining. The pan fills up and there are two floating cut-off switches that shut-off the solenoid when the pan is full of water.

Oh ok, You have the 400A model, I've never been around these, but I've seen a good numbers of people mention about this issues.

jsbigger
12-07-08, 02:18 PM
The flow of water from the saddle to the end of the copper line (disconnected from the solenoid valve) is very strong. Next I connect the copper line to the solenoid valve, and disconnect the plastic line on the outflow side of the valve. I ensure the valve is open, then I turn on the water....and I only get a fast drip.


So do I have a bad solenoid valve?

Jay11J
12-07-08, 04:28 PM
JS,

Is the yellow orifice still in place or no? If no, then I'd say you have a bad valve.

jsbigger
12-07-08, 08:43 PM
The yellow orifice is not in place. I will try a new valve. I ordered the humdifier from an online store, and their policy states that they will not honor warranty claims unless I can show that the equipment was installed by a licensed contractor, or inspected by the city.

Any thoughts on that?

Thanks!!

Jay11J
12-07-08, 09:50 PM
Oh? What online dealer was this? Guess that is the first for me to hear that if they sold it to a DIY'er.

TheCaptain
12-08-08, 08:06 AM
My aprilaire unit came with warranty info that states from the manufacturer that the warranty is void unless installed by a professional. Dont know about the company that sold me mine, but it seems to be Aprilaire's stand on things.

Jay11J
12-08-08, 08:24 AM
My aprilaire unit came with warranty info that states from the manufacturer that the warranty is void unless installed by a professional. Dont know about the company that sold me mine, but it seems to be Aprilaire's stand on things.

Capt,

Many company are like that if their product was sold on line, and the on line dealer should stand behind it since they sold it to the home owners. I know lot of online dealer says they will stand by it...

I know a few people gave me a hard time for not putting in my own furnace, I said I want to be dang sure I got warranty on it, and as well my 10 year parts and labor from Trane. Trane was there for me 3 years ago when I had a crack in my header, and got a brand new furnace out of it.

TheCaptain
12-08-08, 11:00 AM
In their defense, I can't say as I blame them. I more or less muddled through installing my own. I mean, it wasn't that hard or anything, mind you... but I could have easily screwed it up in any number of places if I didn't do a LOT of reading first. Even then, I found my way here for one small question.

Again, thanks for that, Jay.

-Kirk

Jay11J
12-08-08, 03:31 PM
Even then, I found my way here for one small question.

And now that you have found us, you are helping other people in the garden dept!