Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Help: A/C Keeps shutting off
Turtleboy
11-14-08, 05:33 PM
First, I am not a home-technical person at all, so if I use the wrong terms, or describe something incorrectly, I apologize in advance.
I live on the 15th Floor of a large condo in Fort Lauderdale. I don't know how my A/C system works, but I know it's connected to the rest of the building. Here is a picture:
http://farm2.static.flickr.com/1117/1207263161_cde580b64f_o.jpg
http://farm2.static.flickr.com/1252/1208030326_6e2889a671_o.jpg
The A/C runs for about 5 minutes, then I hear it "chug- chug chug....." and then cut off. If I turn off the power wait a few mintues and turn it on again, it will do the same thing.
I've poured a bleach water solution down "the pipe" thingy, and have also tried to run a snake down it. No change.
Any tips?
I live on the 15th Floor of a large condo in Fort Lauderdale. I don't know how my A/C system works, but I know it's connected to the rest of the building. Here is a picture:
http://farm2.static.flickr.com/1117/1207263161_cde580b64f_o.jpg
http://farm2.static.flickr.com/1252/1208030326_6e2889a671_o.jpg
The A/C runs for about 5 minutes, then I hear it "chug- chug chug....." and then cut off. If I turn off the power wait a few mintues and turn it on again, it will do the same thing.
I've poured a bleach water solution down "the pipe" thingy, and have also tried to run a snake down it. No change.
Any tips?
sminker
11-14-08, 06:21 PM
that looks like it is using condenser water suplied by the building when you restart it grab the return(or out labeled copper pipe) and feel it it gets warm if the unit goes off before you feel any heat the pumping from the building might not be running or your strainer on your unit is clogged.that sounds like a building maint. item for them to check.to narrow it down check with a neighbor see if they are running cooling ok.if they are it is probably your condenser supply strainer needs cleaning.large condo would run a system that has these types of connections and that strainer..good luck
Jarredsdad
11-15-08, 01:56 PM
What you have there in the New Towers (serial number tells lots) is a 2 ton water source heat pump.
As sminker said it's probably a water issue. Trane specs 5.5 gpm for this unit. It's most likly going out on high pressure so stop resetting it or you may cause damage YOU will need to pay for.
Top pipe is water out, bottom is water in. I don't see a strainer or solnoid valve. What is the red looking thing behind the door?
Pretty bad water meter install there also.
As sminker said it's probably a water issue. Trane specs 5.5 gpm for this unit. It's most likly going out on high pressure so stop resetting it or you may cause damage YOU will need to pay for.
Top pipe is water out, bottom is water in. I don't see a strainer or solnoid valve. What is the red looking thing behind the door?
Pretty bad water meter install there also.