Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




lkjcjg5
11-10-08, 11:48 PM
I have a 1978 Carrier gas furnace with a Honeywell L4064B fan control limit switch. The thermostat calls for heat, the burners fire up for about 30 seconds, then shut off. I've watched the dial on the limit switch rotate clockwise while the burners are on, then jump forward when it shuts off. I can turn the blower on with the auto/manual knob on the switch. Should I replace the limit switch?


Grady
11-11-08, 07:47 PM
Yes, replace the fan/limit switch. Make sure to get one with the same insertion length.

lkjcjg5
11-12-08, 07:09 PM
Thanks. I removed the old switch to check the length (11 1/2"). When I put it back, it started working again, but it's probably just a matter of time. I've ordered a new one. Thanks again.