Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : heat pump


maryvasq
11-06-08, 08:46 PM
I just installed a 2.5 goodman heat pump split unit. I also bought a 40amps breaker. Will this be enough to operate the system?


doug321
11-06-08, 10:08 PM
Your approach is wrong. You need to look at the nameplate on the heat pump and on the blower unit. They will specify the maximum rated current. This will determine what gauge wire you will need and what size breaker you will need. Using an over sized breaker can result in damaged equipment if the breaker fails to trip or fails to trip fast enough during a fault condition.

maryvasq
11-08-08, 08:39 AM
Thank you Doug. Waht if the heat pump says 60 AMPs max and I have a 40AMPs breaker is that ok?


Ed Imeduc
11-09-08, 10:21 PM
Dont forget you need two breakers One for the outdoor unit and another one for the indoor unit. That has the back up heat for AUX heat and defrost also the blower.;)