Electronic Alarms and Home Security Devices - GE NX-8V2 Installation - Smoke Detector

Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




Joesan
08-19-08, 05:27 PM
I am installing the NX-8V2 alarm system. I do not have a smoke detector. Is there something I should do to SMOKE + and common terminals so that the system will not detct it as an open zone? For example should I put a 3.3 K or 680 ohm resistor supplied with the cotrol board across the terminals SMOKE terminals?

Thanks,

Joe


MrRonFL
08-19-08, 07:35 PM
No, those terminals are for supplying resettable power for 4-wire smoke detectors.

As long as you don't turn on the 2-wire smoke zone function on zone 8, or program a zone for fire, you have no issues.

Joesan
08-19-08, 09:11 PM
Thanks, I think Zone 8 is a defailt for a 2-wire Smoke Detector but I have alarm sensors on it. Do I need to do anything or will the controller sensors?

Joe


MrRonFL
08-20-08, 03:56 PM
The function of _any_ zone is completely dependent on the zone type programmed for it. The default setting for zone 8 on an NX-8 is "instant" (zone type 6).

Zone 8 is the _only_ zone that can be set for 2-wire smokes by removing the jumper on the motherboard, changing the setting on one of the system options in programming, and programming the zone as a fire zone.