Air Conditioning - Trane XE1000 - is this a bulging capacitor?
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Trane XE1000 - is this a bulging capacitor?
saabman
08-18-08, 12:13 PM
re: Trane XE1000 Model # TTR036C100A2
Fan stopped working yesterday. Humming sound with tstat on so turned off. Got inside unit and from reading other related posts hoping it's either my capaciator or contactor.
Pics at website. Is this an example of a bulging capacitor?
http://www.bilhenrygallery.com/temp/index.html
Thx.
Fan stopped working yesterday. Humming sound with tstat on so turned off. Got inside unit and from reading other related posts hoping it's either my capaciator or contactor.
Pics at website. Is this an example of a bulging capacitor?
http://www.bilhenrygallery.com/temp/index.html
Thx.
Gunguy45
08-18-08, 12:28 PM
No A/C guy...but yes, I think so. The only ones I've seen were oval, so the case bulged before the top.
$20 is an easy fix.
You know the procedures to discharge and replace it? Sounds like you've been reading.....
$20 is an easy fix.
You know the procedures to discharge and replace it? Sounds like you've been reading.....
jim-connor
08-18-08, 01:15 PM
No question about it. That capacitor is history.
saabman
08-18-08, 01:17 PM
Thx for responding.
Yes I've several threads on this, but never have tried this before. I found the capacitor online with the specs I need (440 V 45/7.5 mfd) for $45 with S&H. I haven't tried looking for it locally (WI).
You speak of discharge and replace . . . I presume I turn off power, unscrew capacitor unit remove wires and replace as same. Is there more?
Yes I've several threads on this, but never have tried this before. I found the capacitor online with the specs I need (440 V 45/7.5 mfd) for $45 with S&H. I haven't tried looking for it locally (WI).
You speak of discharge and replace . . . I presume I turn off power, unscrew capacitor unit remove wires and replace as same. Is there more?
saabman
08-18-08, 01:32 PM
re: discharge
I read some more and see this is an issue. But do I discharge before I remove the wires or after (of course breaker off etc. so no power coming into unit)?
re: the part
spec sheet says dual capacitor, 440V 45/7.5, w/o resistor. I find these units online but they don't refer to the resistor part. Is this important?
I read some more and see this is an issue. But do I discharge before I remove the wires or after (of course breaker off etc. so no power coming into unit)?
re: the part
spec sheet says dual capacitor, 440V 45/7.5, w/o resistor. I find these units online but they don't refer to the resistor part. Is this important?
Gunguy45
08-18-08, 01:35 PM
Yep....more...unless you maybe like shocks. lol
Turn off power by pulling disconnect or throwing breakers, wait a few minutes, discharge cap by touching across terminals with a screwdriver. Make note of where wires are attached. Go to HVAC supply, get replacement cap
Turn off power by pulling disconnect or throwing breakers, wait a few minutes, discharge cap by touching across terminals with a screwdriver. Make note of where wires are attached. Go to HVAC supply, get replacement cap
saabman
08-18-08, 02:03 PM
Thx gunguy
But just to absolutely clear on this . . . I discharge BEFORE I remove the three wires that are connected to cap?
Thx.
But just to absolutely clear on this . . . I discharge BEFORE I remove the three wires that are connected to cap?
Thx.
mike n
08-18-08, 02:04 PM
Cap is bad for sure and you should replace it but don't just do that clean your outdoor coil as well and tighten up all electrical connections that start thermistor looks suspect you can eliminate it if you like but if you get another one you will have to go to that manufacturers local distributor
Gunguy45
08-18-08, 02:09 PM
Won't hurt anything either way, if you can do it safely.
Since yer contacts are exposed, shouldn't be a problem to put a screwdriver or something with an insulated handle across the contacts on the cap, before removing the wires.
MOST of the time, the voltage dissipates when power is removed. It's just good practice to always discharge caps, esp those with higher voltages.
Oh, and clean off those spiderwebs and make sure the wires are seperated well, when you put in the new one. Hate to have the vibration rub thru the insulation.
Since yer contacts are exposed, shouldn't be a problem to put a screwdriver or something with an insulated handle across the contacts on the cap, before removing the wires.
MOST of the time, the voltage dissipates when power is removed. It's just good practice to always discharge caps, esp those with higher voltages.
Oh, and clean off those spiderwebs and make sure the wires are seperated well, when you put in the new one. Hate to have the vibration rub thru the insulation.
saabman
08-18-08, 07:11 PM
Thanks all for help. Bought cap, installed it, and all seems well. Good news because it is very hot and humid tonight. Indoor temp 82 when I powered it up again.
Again, appreciate the tips.