Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




graphixv
08-04-08, 08:44 PM
Kind of in a pickle.

The building where I am at has 4 fire zones in it. Four lines coming in with apparently some 2 wire smoke and heat detectors plus fire pulls on each line.

I had to remove an existing box because of the age. Looking at the Vista-100 manual, it only appears that it takes 2 fire zones with 2 wire detectors with 16 detectors each zone. I probably do not more than that (32) in the building. They are just divided up into four different wires.

I am not planning to use the box for burglary right now. Only fire. Am I right assuming that I can not wire the 2 other smoke detector wires into other zones on the Vista-100? If not, I may have to rewire to make two large fire zones (a pain).


Thanks
GRX


PRO1 TECH
08-05-08, 05:08 AM
how about make them polling loop units then all units will there own zone :thinker:

http://www.watchdogsuperstore.com/index.asp?PageAction=VIEWPROD&ProdID=380

MrRonFL
08-05-08, 05:48 AM
Sadly, that will not work with 2 wire smokes, without replacing the detectors with polling loop (addressable smokes).

What you _can_ do is use a 2-wire to 4-wire conversion module.


kcxj
08-05-08, 04:53 PM
Putting a sim module on each smoke with allow for a vplex data loop as pro1tech advised. You will need 1 sim module for each smoke.

MrRonFL
08-05-08, 07:40 PM
Ummm, fellas, the 4139sn _cannot_ suppply power to a _two-wire_ smoke. It is for monitoring a dry contact device.

Yes, you could use it to monitor a _4-wire_ smoke, but you would still have to supply power to the smokes.

Sorry, but it _cannot_ work for 2-wire smokes.