Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




11-26-00, 07:16 AM
Brief history: Mobile, Al; bought 13 year old house last August; had "A" coil replaced June 2000; fan would not shut off last week replaced contactor in air handler, fan operating ok; now when calling for heat contactor in air handler clicks, clicks, clicks until manually reset of thermostat to cause electric strip heat to come on, clicking starts again when system gets close to being satisfied and tries to shut down. Any suggestions on what to check next, have voltmeter will test.


fjrachel
11-26-00, 10:30 AM
Remove t'stat and jumper the heat circuit. If it works normally, replace stat. If not, check complete control circuit.

R-12guy
11-26-00, 11:18 AM
I would tend to think that the Contactor has a weak coil... or a loose conection ..


11-26-00, 09:04 PM
Thanks for replies. T'stat checked out o.k. Problem seems to be the defrost relay in the outside unit. It was clicking in sinc with inside relay and had a burnt contactor. Will replace on Monday and let you know if heat pump starts working correctly. Also checked 24v transformer and was getting a 21.4v reading is this o.k. or should it be closer to 24v? Thanks again!

PDF
11-28-00, 05:05 PM
Please check the voltage to your system when it is running.Some units have a "TAP" on the board for running 208 or 240 volts.Whats the difference?I like 2 see at least 24.6 volts from the transformer.Check your volts and shift the transformer "TAP" to the correct voltage.PDF