Kitchen Gas Appliances - Hooking up 2 to 3 Appliances to LP
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Hooking up 2 to 3 Appliances to LP
limberis
02-12-08, 11:33 AM
Hi,
I currently have one gas range connected to a 50 gal propane tank. The previous owner of my house connected it with copper pipe (looks like 3/8"). I want to install an additional gas range in my house.
What is the best way to connect the second range? Do I split the line in the house before it reaches the other range or do I branch off outside just off the tank? Both ranges are about 30 feet from the tank.
Is a 50 gal tank large enough? In the future I would also like to connect a gas dryer. Is the 50 gal tank large enough for all three appliances?
Thank you for your time. This is my first time on the site and I am very impressed with it. What a great service.
Sincerely,
Pablo
I currently have one gas range connected to a 50 gal propane tank. The previous owner of my house connected it with copper pipe (looks like 3/8"). I want to install an additional gas range in my house.
What is the best way to connect the second range? Do I split the line in the house before it reaches the other range or do I branch off outside just off the tank? Both ranges are about 30 feet from the tank.
Is a 50 gal tank large enough? In the future I would also like to connect a gas dryer. Is the 50 gal tank large enough for all three appliances?
Thank you for your time. This is my first time on the site and I am very impressed with it. What a great service.
Sincerely,
Pablo
hankhill6018
02-12-08, 02:48 PM
The good news is the 50 gallon tank should be enough for the 3 appliances. The bad news is 3/8 inch OD copper tubing is not.
I just had a service call with similar circumstances. With 2 ranges hooked up to the propane supply with 3/8 inch tubing, the customer was only getting about 3/4 the required pressure for the appliances to run properly.
There are two ways to remedy this:
1) Replace the existing gas line with something more suitable. I would not go with anything less than 1/2 inch iron pipe size.
2) Have your propane supplier convert what is likely a 1/2 pound system to a 2 psi system. This will utilize the same gas line but increase the pressure entering the house then dropping it down to a working pressure at the appliances.
I just had a service call with similar circumstances. With 2 ranges hooked up to the propane supply with 3/8 inch tubing, the customer was only getting about 3/4 the required pressure for the appliances to run properly.
There are two ways to remedy this:
1) Replace the existing gas line with something more suitable. I would not go with anything less than 1/2 inch iron pipe size.
2) Have your propane supplier convert what is likely a 1/2 pound system to a 2 psi system. This will utilize the same gas line but increase the pressure entering the house then dropping it down to a working pressure at the appliances.
Ed Imeduc
02-12-08, 03:02 PM
Ill go with the gas line size has to be bigger. Also with 3 units on at the same time . No that 50 gal tank wont do it. If its cold outside it cant burn off the gas as fast to give gas to 3 units .Tank 30 ft from the home. You can put a little joe regulator on the tank run that 3/8" line to the home and a new low regulator then go with 1/2" line and 11" W/C to the ranges
limberis
02-22-08, 10:16 AM
Ed and Hank (I love King of the Hill!),
Thanks so much for your replies. That gives some ideas on my options and where to go next. I do have another question but will post that separately. Since I live in a duplex with my inlaws it might make sense to have two separate tanks in stead.
Sincerely,
Pablo
Thanks so much for your replies. That gives some ideas on my options and where to go next. I do have another question but will post that separately. Since I live in a duplex with my inlaws it might make sense to have two separate tanks in stead.
Sincerely,
Pablo