Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Heat Pump Tonnage


bignick
12-19-07, 09:27 PM
I am replacing my heat pump. I need to find out the current tonnage that my Heat Pump unit is. I have a Carrier, model 38cq039340. I believe the unit is 25 years old. Any help would be appreciated


Jay11J
12-20-07, 06:15 AM
It looks like it's 3.5 ton.

If you are getting a new system, the dealer should do a Manual-J(Load Calc.) on your home. Your home I'm sure has been updated over the years with new windows, attic insulations... ect..

pflor
12-25-07, 10:02 PM
As per manufacturer literature, your unit ratings are as follows:

Cooling mode capacity: 34,500 Btuh (at 95F outdoors)
Heating mode capacities:
37,500 Btuh (at 47F outdoors), and
22,000 Btuh (at 17F outdoors)

Heat Pump sizes are determined by their cooling capacities. Your unit is then a 3-ton.

But I could not agree more with Jay11J. A heating/cooling load calculation should be done. A tit-for-tat replacement is not the best way to go. Far be from it.