Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




pstar
08-20-07, 09:25 PM
The outside Carrier unit (12-13 years old) is kicking on, but the air blowing out the top isn't hot at all. I jabbed one of the freon fittings and there's plenty of pressure. Also, the air is flowing through the ductwork fine. However, none of the copper pipes are changing temperature.

What should be my next step?


flirty1
08-20-07, 10:04 PM
are you sure the compressors working.

pstar
08-21-07, 06:42 AM
I'm not sure the compressor is working. How can I check?


mattison
08-21-07, 09:02 AM
Normally if the two copper pipes are the same temp and around ambient temp it is not running.

What you can do is turn off the power to the outdoor unit, remove the service panel and inspect your wiring and take a good look at the capacitor and see if it's buldging.

pstar
08-21-07, 09:06 AM
I remember the capacitator looking old and worn out (surface rust), but nothing out of the ordinary. I imagine a bad cap would look like a swollen AA battery (larger, of course), right?

Would I be able to get a cap at HD/Lowes?

Ed Imeduc
08-21-07, 09:40 AM
For a capacitor try any AC shop, Supply company or electric shop. They can look good and still be bad

pstar
08-21-07, 01:39 PM
Thanks guys! It was the cap.