Electronic Alarms and Home Security Devices - Do smoke detectors and heat detectors connect to the same circuit?

Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




rchalk
08-05-07, 02:59 AM
I am installing 4-wire smoke detectors, and two-wire heat detector (Kitchen) to a Power 832 system. Do these devices both connect to the same circuit? On the smoke detectors, I assume two wires are for power, and two are for detection. Would I use the detection wires for the heat detector?

Thanks,
Richard


HotinOKC
08-05-07, 09:09 AM
From just looking at the install manual you need to connect each of these detectors to each other, then have the last detector connected to a "Z" terminal on the board and the other on any "COM" terminal.

The two power wires will go to "AUX" and the other one to "PGM 1 or 2"

You will need a EOL resistor as well.

Here is the installer manual for your panel. Look at section 2.9.4

http://nextalarm.net/Files/5010im.pdf

I'm sure you will get more input soon as well.

MrRonFL
08-05-07, 05:38 PM
Yes, you may put the heat detector in the circuit. You would only use the alarm loop pair, of course. The heat detector is just a heat actuated normally open switch.


Integrator97
08-07-07, 09:55 PM
You should also have a power supervision relay connected at the last smoke detector. THis monitors the power on a 4 wire smoke loop, and if the power goes away, breaks the detector or zone circuit, causing a trouble.