Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Installed Thermal Expansion Tank, PRV still leaks occasionally
leelai
12-04-06, 08:59 AM
Just installed a new Thermal Expansion tank this weekend and also replaced the PRV on my 40 Gallon water heater. After installation, it helped out a whole lot and the PRV only dribbles a little bit occasionally, after the pressure has built up for a couple hours.
My question is, what could be wrong? I thought a Thermal Expansion tank would resolve the issues of expansion and the leaking PRV? Could I have precharged the tank incorrectly? Maybe I just need a bigger tank? What else could need fixing?
My question is, what could be wrong? I thought a Thermal Expansion tank would resolve the issues of expansion and the leaking PRV? Could I have precharged the tank incorrectly? Maybe I just need a bigger tank? What else could need fixing?
mbk3
12-04-06, 11:43 AM
you may want to take the water pressure at a hose bib
leelai
12-04-06, 12:48 PM
Did that, and looks like water pressure still builds up to 140 or so
shacko
12-07-06, 10:33 AM
Did that, and looks like water pressure still builds up to 140 or so
140 lbs is way too high, you need a pressure reducing valve, most codes require a max. of 80lbs. Most PRV valves are set for 150lbs, it takes very little thermal expansion to exceed that limit when you start with 140psi..
The tank should be charged to the incoming water pressure, but with your excessive pressure this does not apply.
Bottom line is you need a pressure reducing valve, make sure that you have a pressure gage on the supply side of the prv. Lots of luck.
..............................................................
"If all else fails, read the directions"
140 lbs is way too high, you need a pressure reducing valve, most codes require a max. of 80lbs. Most PRV valves are set for 150lbs, it takes very little thermal expansion to exceed that limit when you start with 140psi..
The tank should be charged to the incoming water pressure, but with your excessive pressure this does not apply.
Bottom line is you need a pressure reducing valve, make sure that you have a pressure gage on the supply side of the prv. Lots of luck.
..............................................................
"If all else fails, read the directions"
Beachboy
12-07-06, 01:38 PM
Is your normal operating pressure 140#, or just when the system is bottled up and the water heater is operating? Also, are you served by a municipal water system or do you have your own well?
If you're on a municipal system, do you know if they have a pressure reducing valve or backflow preventer on your incoming water line that is not allowing the thermal expansion to backpressure into the municipal distribution system?
If you're on a municipal system, do you know if they have a pressure reducing valve or backflow preventer on your incoming water line that is not allowing the thermal expansion to backpressure into the municipal distribution system?
leelai
12-12-06, 09:45 AM
It builds up to 140 after not using it for a while and the water heater cycles. normal operating pressure is about 40. I thought installing a expansion tank would fix it but the problem continues. I am on municipal water and there is a pressure reducing valve, however, which is why I'm thinking it's a bad PRV?
Ed Imeduc
12-12-06, 09:52 AM
How high do you have the water heater set at. 40 psi water to 140 psi after the water is on. Dont sound right. The tstat in the heater ok????
leelai
12-12-06, 11:35 AM
water heater temp is set to below the "normal" setting mark on the dial, and i measured it to be about 125 degrees.
Ed Imeduc
12-12-06, 11:54 AM
Just installed a new Thermal Expansion tank this weekend and also replaced the PRV on my 40 Gallon water heater.
Ok Did you check the air side of the tank before you put it in??????? With no water pressure on it . The air side should have 38lb psi in it
Ok Did you check the air side of the tank before you put it in??????? With no water pressure on it . The air side should have 38lb psi in it
leelai
12-12-06, 12:33 PM
Yup. Checked the air pressure in the tank before and made sure it was right at 40ish.