Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Announce-only zone type?


jlindema
10-20-06, 08:59 PM
Hi all-

I thought I had everything figured out with regard to configurable zone type 90, on my Ademco/Honeywell Vista-20P system.

It may sound strange- but I would like to configure a zone type that does nothing more than chime at the keypad when the zone is activated and restored. I would like for it to chime (announce a 'change' via chime) during all modes (away, stay, night, disarmed). No alarm, no reports -just chime.

Using the configurable zone types worksheet, I configured *182 like so:
0 0 0 0 0 0 0 0 0 4

I successfully enrolled a 5816 loop 2 -using a zone type of 3 for testing. Worked perfectly...chimed as expected, displayed fault on the keypad, etc.

I then changed this zone's type to 90.
After doing so, I no longer got any faults displayed on the keypad- and, as you may have guessed- no chime :(

Any advice would be greatly appreciated.
Thanks,
John


MrRonFL
10-20-06, 09:37 PM
I think you need the sequence:
0 7 0 3 0 3 0 0 0 4

This tells it to fault in all arm/disarm conditions, with auto reset and chime when chime enabled. The zone fault will display on the keypad. The zone must fault to activate the chime.

jlindema
10-20-06, 10:22 PM
Thanks again MrRonFL!

About 1 min. before I saw your reply, I tried:
0 3 0 3 0 3 0 0 0 4 -and thought I had it.

Seeing your reply and making the second digit a 7
-it now works exactly as a need.

Awesome!