Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




BigDog4All
08-27-06, 12:01 AM
The air conditioner was working fine...then this afternoon, I noticed the temperature raising in the house. Well this is what I found...

1. Furnace turns on normal...motor fan turning..blowing out warm air...not cool.
2. 24 Volts is at the AC Unit.
3. 220 Volts is good coming in.
4. Pressed contacts button.
5. 220 Volts was tranferred.

Contacts not closing when 24 volts is applied.
No AC fan is turning, even when I press contacts. But there is a slight spark.
No compressor starts, even when pressing contacts. There is a little grunt sound when pressing contacts.

How can you tell if the capacitor is bad? Is there a test for the capacitor? How do you tell if the compressor is bad? It's a Lennox model, about 16 years old.

What other tests can I perform?

Thanks...


Ed Imeduc
08-27-06, 09:52 PM
Contacts not closing when 24 volts is applied.
Do you have a low psi cut out or a high head reset????

No AC fan is turning, even when I press contacts. But there is a slight spark.
No compressor starts, even when pressing contacts. There is a little grunt sound when pressing contacts..
For the cost try a new start run cap there.
How do you tell if the compressor is bad. Pull the wires off it and Ohm it out and to ground.

ED