Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Another Heat Pump stopped working
rwilson
08-16-06, 09:03 AM
Basically everything seemed to be working when I got home. But at some point last night I noticed the air coming out of the vents was not cold. I checked the drain for the unit the basement, it was not draining, but it was not plugged up either. I turned off the power for 10 minutes, turned it back on and it still didn't work. There is no icing on the lines inside or outside. The unit/fan outside is not turning, it is making a humming noise. The fan turns if you push it, so it does not appear the fan motor is locked up. I have called for a technician, but I would like to know the possibilities of what the problem could be. Thanks for any help.
gmichaelp
08-16-06, 10:38 AM
If its humming...sounds like your getting 24v. Its probably gonna need a new capicator.
Ed Imeduc
08-16-06, 12:52 PM
Like said the hmming can mean you are getting 24 V. From there can just be the contactor or the contactor points dont close . Then on to the capacitor. But you said the fan didnt run when you pushed it and calleing for cool so its back to the contactor. have you turned the breakers off and back on??
ED
ED
rwilson
08-16-06, 02:57 PM
I was not there, but the technician came out and told my wife it was the condensor. Its working now. Thanks for the suggestions.
Ed Imeduc
08-16-06, 04:37 PM
That dont say what was wrong .Or what he charged you for. The condenser is the whole big thing outside .
ED
ED
thecut
08-16-06, 05:47 PM
Basically everything seemed to be working when I got home. But at some point last night I noticed the air coming out of the vents was not cold. I checked the drain for the unit the basement, it was not draining, but it was not plugged up either. I turned off the power for 10 minutes, turned it back on and it still didn't work. There is no icing on the lines inside or outside. The unit/fan outside is not turning, it is making a humming noise. The fan turns if you push it, so it does not appear the fan motor is locked up. I have called for a technician, but I would like to know the possibilities of what the problem could be. Thanks for any help.
Well the humming is the compressor running, which is a good thing. If the fan isnt turning with the power on, i would venture to say that its a electrical problem with the fan, perhaps a capacitor or the fan itself is grounded/shorted. Its probably shutting off on a low pressure/high pressure control after a short period of time.
Well the humming is the compressor running, which is a good thing. If the fan isnt turning with the power on, i would venture to say that its a electrical problem with the fan, perhaps a capacitor or the fan itself is grounded/shorted. Its probably shutting off on a low pressure/high pressure control after a short period of time.