Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : CA Compressor Hard Starting
meverly
07-10-06, 04:23 PM
Hello,
I just had a new 5 ton Evaporator coil put in due to the old one's drip pan was rusted through. Other than that system ran fine.
A few days after installation the outside compressor wasn't starting. Service Repairman stated capacitor was bad. My unit took a "60" but all he had was a "50" so he installed that with a Hard Start Kit (Ordered "60" to be replaced when it came in).
This worked for a few days the it doesn't want to start again.
Different Service Repairman comes out and installs a "50" & "10" along with the Hard Start Kit that was left in place. Says no need to put in the "60" when it comes in.
This works for a few days and now its starting intermittantly
again. Service Repairman says it's just an old compressor
and is ready to go.
I don't dispute that it is old but I"m looking for an answer as to
why no problems before the evaporator was replaced.
The new evaporator is considerably taller than the old one.
I'm assuming (guessing) that this would require a greater volume of Freon, thus making it harder for the compressor to start?
Nobody seems to have an answer.
I appreciate any opinions! Thanks!
Mark
I just had a new 5 ton Evaporator coil put in due to the old one's drip pan was rusted through. Other than that system ran fine.
A few days after installation the outside compressor wasn't starting. Service Repairman stated capacitor was bad. My unit took a "60" but all he had was a "50" so he installed that with a Hard Start Kit (Ordered "60" to be replaced when it came in).
This worked for a few days the it doesn't want to start again.
Different Service Repairman comes out and installs a "50" & "10" along with the Hard Start Kit that was left in place. Says no need to put in the "60" when it comes in.
This works for a few days and now its starting intermittantly
again. Service Repairman says it's just an old compressor
and is ready to go.
I don't dispute that it is old but I"m looking for an answer as to
why no problems before the evaporator was replaced.
The new evaporator is considerably taller than the old one.
I'm assuming (guessing) that this would require a greater volume of Freon, thus making it harder for the compressor to start?
Nobody seems to have an answer.
I appreciate any opinions! Thanks!
Mark
mattison
07-10-06, 04:28 PM
It's possible that they overcharged it.
How old is the outdoor unit ?? You may still need the hard start kit.
How old is the outdoor unit ?? You may still need the hard start kit.
meverly
07-10-06, 04:59 PM
mattison,
Thanks for the reply. The unit is old, about 14 years in service.
Each time the service guys were out here they put the gauges on it and said it looks fine.
Do you think that since it's old perhaps it would start better if
it was a little undercharged? (They mentioned before they replaced the evaporator coil that it was a little low on Freon,
but not much).
Can an end user such as myself "bleed" some off?
Thanks for the reply. The unit is old, about 14 years in service.
Each time the service guys were out here they put the gauges on it and said it looks fine.
Do you think that since it's old perhaps it would start better if
it was a little undercharged? (They mentioned before they replaced the evaporator coil that it was a little low on Freon,
but not much).
Can an end user such as myself "bleed" some off?
mattison
07-10-06, 05:03 PM
Can an end user such as myself "bleed" some off?
No you sure can't.
They need to check the charge by using subcooling or superheat depending on the metering device not just looking at the gauges.
No you sure can't.
They need to check the charge by using subcooling or superheat depending on the metering device not just looking at the gauges.