Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : No Hot Air
Jonathan
07-10-06, 09:44 AM
Hi folks was wondering if anyone could help me out with this. My A/C just kicked it last night .
Symptoms:
Unit is blowing out unconditioned air (not cool, literally and figuratively)
Trouble Shooting:
Filter is new and doesn’t need cleaning
No Freezing on either line
Lines are nether hot nor cold
Condenser fan is running fine when tripped by the thermostat
Air flow is great
Condenser unit is clean and clear of debris
Don’t hear compressor kicking on, or trying to kick on.
History:
Last session the duel capacitor was replaced
Unit must be close to 20 years old
Questions:
Could it be the capacitor again?
Is my compressor shot?
Could it need more refrigerant? If so does that indicate a leak in the lines?
Symptoms:
Unit is blowing out unconditioned air (not cool, literally and figuratively)
Trouble Shooting:
Filter is new and doesn’t need cleaning
No Freezing on either line
Lines are nether hot nor cold
Condenser fan is running fine when tripped by the thermostat
Air flow is great
Condenser unit is clean and clear of debris
Don’t hear compressor kicking on, or trying to kick on.
History:
Last session the duel capacitor was replaced
Unit must be close to 20 years old
Questions:
Could it be the capacitor again?
Is my compressor shot?
Could it need more refrigerant? If so does that indicate a leak in the lines?
Ed Imeduc
07-10-06, 09:57 AM
Don’t hear compressor kicking on, or trying to kick on.
[QUOTE]Questions:
Could it be the capacitor again? COULD BE
Is my compressor shot? YOU SAY IT DONT RUN ,CAN BE HAVE TO CHECK IT OUT
Could it need more refrigerant? DONT KNOW TILL THE COMPRESSOR RUNS
If so does that indicate a leak in the lines? CANT TELL YET IS THIS THE FIRST GAS IN 20 YEARS??
This is one of the best post with info in it that I have seen in a longtime.
ED:D :thumbup:
[QUOTE]Questions:
Could it be the capacitor again? COULD BE
Is my compressor shot? YOU SAY IT DONT RUN ,CAN BE HAVE TO CHECK IT OUT
Could it need more refrigerant? DONT KNOW TILL THE COMPRESSOR RUNS
If so does that indicate a leak in the lines? CANT TELL YET IS THIS THE FIRST GAS IN 20 YEARS??
This is one of the best post with info in it that I have seen in a longtime.
ED:D :thumbup:
Jonathan
07-10-06, 10:52 AM
Thanks for the quick response Ed. I will check the capacitor first thing when I get home. It was late and dark last night and didn’t fell like pulling apart my unit under my deck. Again, as far as I can tell (no sound when engaged by the thermostat) the compressor does not or is not trying to turn on. If it was low on refrigerant or having a leak would it still be trying to kick on
Ed Imeduc
07-10-06, 11:10 AM
didn’t fell like pulling apart my unit under my deck.
Is this new ????? if unit blowes up it needs about 6ft clear above it??????
Even with a low switch cut out it should just try and start for a little bit
ED;)
Is this new ????? if unit blowes up it needs about 6ft clear above it??????
Even with a low switch cut out it should just try and start for a little bit
ED;)
Jonathan
07-10-06, 12:13 PM
It actually sits right next to my deck but the fuse box and lines all run under my deck.
Jonathan
07-10-06, 12:16 PM
I originally thought that if my capacitor was dead my condenser fan would not work, but my compressor would try until it overheated. Is the opposite true? Can a bad capacitor let the fan run but the compressor not?
mdtaylor
07-10-06, 12:36 PM
Yes, it can. It could also be the contactor. A 20 year old unit sometimes broke only one leg of the 240v going to the compressor so if one side of the contactor goes to the fan and the other to the compressor, and the side going to the compressor goes bad then the fan will run but the compressor will not.
Jonathan
07-10-06, 05:32 PM
Thanks for all your help guys. It seems the cluprit was a a fried wire/connectoin at the capasitor.
Another mystery solved at Doityourself.com