Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




pathannifin
12-02-05, 09:35 AM
Request any advice:
less than 1 year old, attic unit Ducane 1.5 Ton :)
(house has 2 units, one up, one down)
in heat mode, unit trips off main 30amp breaker in about 4 minutes. If I set thermostat to emergency heat, it does not trip breaker, but no heat is generated although blower keeps on blowing.... nice cold air. No sign of heat stip doing anything nor the compressor unit.
(NOTE: I don't see my compressor fan working on the downstairs unit either, so I'm guessing it is all heat strips? or can the compressor work without the fan?)

Inside the unit all looks to be wired properly, it worked fine a few weeks ago, and the air works great.

Any ideas? please?


lenny56769
12-05-05, 07:49 PM
call a tech you have to many amps being pulled some were

DNT1
12-06-05, 11:04 AM
Probably need a tech on this but there are a couple of things you can check yourself if you like. 1. Set the thermostat to heat and go out to the outside unit see if you can determine if the compressor is running or not 2. If compressor is determined to be running take a stick and give the condensor fan a push to see if it will start turning (also push it to see if it is hard to turn locked up) Report back results ASAP.