Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : ac humming


qtip
09-15-05, 06:04 AM
here is my problem. air in house is hot. Went outside and unit has a low humming sound. Blade does not turn. Any advise?


DNT1
09-15-05, 12:09 PM
A lot of units use a dual capacitor which controls both the condensor fan and compressor if niether the fan nor compressor is running when the thermostat is calling for cooling and unit is producing a humming sound it is likely the capacitor, replace it and report back.

qtip
09-15-05, 06:59 PM
a friend came by and we checked unit. We took panel off and pushed a switch and unit started. he said the problem is relay switch. Is this the same thing as a capacitor? Also cannot find name of unit. All it says is, SUPER HIGH EFFICIENCY 7000. On inside it says by INTER-CITY PRODUCTS? HELP!!!!


DNT1
09-15-05, 08:06 PM
Well if it was the contactor that he pushed and the unit came on, it is technically a electromechanical relay does it look like this? http://toad.net/~jsmeenen/contactor.html

Sambolino
09-18-05, 05:46 PM
I'm encountering similar problems. When the system calls for cooling, the outside unit 'hums' and the fan blades don't spin. If I start the blades spinning, all is well and the unit operates just fine. So, I'm guessing it's not the fan motor but the 'switch' that starts the fan motor. Is this a capacitor issue?

DNT1
09-18-05, 07:43 PM
Big S yours sounds like a capacitor problem check out this site for some capacitor info might help you locate yours http://www.yorkcapacitor.com/products-motor%20run.html

mattison
09-19-05, 05:14 AM
You need to get a voltage reading on the control side of the contactor to verify whether or not you have 24 volts present.

Sambolino
09-19-05, 06:21 AM
Thanks DNT1 and mattison! I'm expecting (when I open up the unit) to find a bulging capacitor. Since I can get the unit cooling by manually turning the fan blades (before the compressor cuts off), is this a 'start' cap issue? :confused:

mattison
09-20-05, 05:25 AM
Your problem indeed sounds like a capacitor. Make sure you turn off the power to the unit before getting in there and dischage the capacitor by shorting across its terminals with a well insulated screwdriver before touching it.