Air Conditioning - Compressor wont turn off
Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : Compressor wont turn off
tjm339
09-05-05, 12:54 PM
Compressor was not turning off on a 30 yr. old Carrier unit. I replaced the contactor and problem was fixed for a week now problem is back. Any ideas?
Jay11J
09-05-05, 03:47 PM
Do you know if you are getting power at the contactor at all times?
tjm339
09-05-05, 10:50 PM
I have to check. This is a old system and the contactor is controlled by 240 volts
tjm339
09-06-05, 10:51 AM
There is no voltage at the coil. I get 240 volts at bottom of contactor but none on top I cant figure how is this fan getting power. Anyone ever run into this?
tjm339
09-06-05, 12:13 PM
inside the unit I have a
Start Relay
Control Relay
Holding Relay
Contactor
Indoor Fan Realy
Transformer
Timer Motor
I replaced the contactor, but problem came back in a week
Start Relay
Control Relay
Holding Relay
Contactor
Indoor Fan Realy
Transformer
Timer Motor
I replaced the contactor, but problem came back in a week
Ed Imeduc
09-06-05, 12:22 PM
If you pull the Y wire off at the tstat does the outside unit still run??????
This is a old system and the contactor is controlled by 240 volts
I go back that far and then all units worked off 24V for the controls. That is unless you have a Com. set up here
ED ;)
This is a old system and the contactor is controlled by 240 volts
I go back that far and then all units worked off 24V for the controls. That is unless you have a Com. set up here
ED ;)
tjm339
09-06-05, 01:35 PM
Yes if I take off the Y wire it still runs. The problem now happens abut half the time. There is a transformer in unit that sends out 24 volts to the control relay. I think the control relay is my problem. Is there any way I can test it before buying a new one?
Ed Imeduc
09-06-05, 01:38 PM
Yes just pull one leg of the 24V to it off and see if it drops out
ED ;)
ED ;)