RogerK
06-23-05, 06:47 PM
Can anybody think of a plausible reason why a system would be pumping foam (as viewed through sight glass on high pressure line) when it's not undercharged?
The system (Trane XE-900) hasn't cooled particularly well for years, and never reaches set temp on hot (90+) days. Discharge air temp is rarely more than ~10 degrees below room temp even on the mildest days. I had a filter/dryer and sight glass installed in April, and a triple evac done on the notion that the system might have had moisture from the beginning. In March, both the A-coil and the condenser were THOROUGHLY cleaned.
The tech can't explain the foam in the line. All he says is it must be something with the A-coil (??). There is no THX valve. He swears the system is not undercharged. Is it possible for the A-coil orifice to have become larger than it's supposed to be? The unit is 17 years old.
Pressure & temp readings today:
Low side 76
High side 160
Outside air temp 81
Inside air temp 73 (no wet bulb therm avail)
discharge air temp 62
Static press (unit off 5 minutes) 102 (both sides)
Thanks for any ideas.
The system (Trane XE-900) hasn't cooled particularly well for years, and never reaches set temp on hot (90+) days. Discharge air temp is rarely more than ~10 degrees below room temp even on the mildest days. I had a filter/dryer and sight glass installed in April, and a triple evac done on the notion that the system might have had moisture from the beginning. In March, both the A-coil and the condenser were THOROUGHLY cleaned.
The tech can't explain the foam in the line. All he says is it must be something with the A-coil (??). There is no THX valve. He swears the system is not undercharged. Is it possible for the A-coil orifice to have become larger than it's supposed to be? The unit is 17 years old.
Pressure & temp readings today:
Low side 76
High side 160
Outside air temp 81
Inside air temp 73 (no wet bulb therm avail)
discharge air temp 62
Static press (unit off 5 minutes) 102 (both sides)
Thanks for any ideas.