Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Thermostat acting up.....I think


wtavcar
02-15-05, 01:16 PM
I have a White-Rogers 1F82-54 Programmable Thermostat attached to a YORK Olympian 14 (14 SEER & 9 HSPF) & Chromolax HAF-324D (24kw) electric Furnace.
I have been having strange behaviour lately with the programming. It would appear that it is unable (lately) to bring the temp. back up to (23C/73F) from the setback temp (21C/70F) during the night. This only happens when the outside temp is at certain amount.

When in normal HEAT mode and the temp hovers above or around 0C(32F) +/- 5C(9F), It is OK. Once the temp is around -10C(14F) +/- 5(9F) then it can take forever to come up. Below -15C(5F) (obviously) the furnace only runs. When it's furnace only then all is OK.

This past weekend is a prime example. I purposely backed up the startpoint 2 weeks ago after it started acting up, to 4:30 AM to ask it to go from 21 to 23. By 7AM it was still showing 21C(70F). It was -11C(12.2F) Sunday AM. I gave up and put it to emergency to bring it up. Once up I put it back to normal heat.

If I understand the thermostat owners manual, it moves the startpoint so that the temp. (some sort of smart technology) will be at the requested value at the designated time. If it misses it keeps adjusting until it hits it.

If I assume that most times it kicks in ~30 min.
prior (per the manual) to setpoint my system therefore ran 2.5+ hrs.? Does not the thermostat have a logic built in so that after a certain time, it gives up trying and the
furnace kicks in? I believe it does because I have noticed it do it. Could this "decision-making" circuit be faulty?

By-The-Way: I live in Montreal Canada. It gets cold here in the winter, as you can see by the temperatures I am describing above.

I have been to my local Home-Depot and saw HONYWELL replacmeent thermostats. If it's only that I would change it myself, instead of calling service, and be charged double. They (thermostats) appear simple to change.

Diagnostics already done:
=====================================

+ the filter is cleaned religiously every 30 days. I have a
electrostatic filter, so no airflow blockage.

+ I put my hand on the large copper tube (near the furnace) leading from the heat pump to the furnace. I cannot keep my hand on it from the heat, so the heatpump is definitely OK.

+ With the thermostat set to "emergency" it works like a charm. The furnace is therefore OK.

============

Just as added information the house was built in 1967 so the R-value of the house is a big question. I have been fighting with the idea of fluctuating the temp. or keeping it steady (because of the low insulation). By the way the heat pump was installed in 2000, the furnace in 1976.

The electric furnace is a 24Kw furnace. My house (30x40 semi-detached duplex) is 2 floors of 1200sq.ft. The lower (basement) has 400 sq.ft. (in-house) as garage. The garage is downhill into the basement level. That means that 1200 (top) + 800 (basement). The basement is finished by the way. The garage is heated independently but set low.

============

As an aside question !

(1) I have read different opinions about programmable thermostats and that they are not good for heatpump systems.
Comments ?

=====================================

Any idea why this is happening ? Is it worth it to change the thermostat? This would be the 2nd WR brand I change. I am tempted to get a HONEYWELL instead. :wall:


mattison
02-15-05, 03:48 PM
In my opinion I would dump the programmable stat. It don't save you any money on a heat pump.

When the setback is over does the auxilary light come on with the heat pump?? How is your stat wired?

Grady
02-15-05, 06:42 PM
I agree with Mattison about the programable stat (even one with "smart technology") & a heat pump. Most economical to operate a heat pump is to "set it & forget it" regarding the thermostat. I suspect your stat is not wired correctly for your system, you have a malfunctioning outdoor thermostat (if so equipped), or a relay problem in the air handler.


scottg
02-16-05, 05:26 PM
Honeywell thermostats do have smart technology that computes the temp drop and rise and the time that it takes to satisfy the thermostat. Then it starts the heat pump early to achieve the temp desired at the time desired without cycling the strip heaters. But if the outdoor temp is low then that heat pump is going to work til the cows come home period.

So I do like the Honeywell thermostat but you need to judge it from a year round season and therefore I do promote them.

wtavcar
02-18-05, 06:11 AM
OK Folks,

1) Here is the wiring at the thermostat:

[ letter : Wire color connected {description from manual}]

C : Black Wire { Common }
G : Green Wire { Fan }
R : Red Wire { Power }
O/B : Orange Wire { C/O Valve } (*)
Y : Yellow Wire { Compressor }
W2 : - NONE -
E : - NONE -
L : Blue Wire { Monitor }

(*) Set to "B" on the unit.

Just an FYI. The unit outside does have some sort of metalic bulb attached to the unit. I assume some sort of temp. sensor.

2) I am puzzled why the W2/E are empty!

3) Understanding what I have read so far, it would appear that this varying the start time theory is flawed. Our temps around here can fluctuate wildly within 12-24 hrs. That said the system would constantly be guestimating the start time.

Comments?

Grady
02-18-05, 06:27 PM
W2 & E not having any connection seems to indicate there is no auxilary heat wired thru the thermostat. If this system is new, I would call the installer & ask to have someone come out or at least explain the lack of connections.
I stand by my comments about programable t-stats & heat pumps, particularly in your area.

wtavcar
02-19-05, 06:09 PM
My mistake, :wall:

With the mess of wires thru a small hole I did not notice that there was a wire on the`E` post. The W2 is empty.

I am looking at the HONEYWELL RTH8500D (at Home DEPOT). It used to work fine. It started acting up this heating season. Therefore the reason for the questions.

I We are accustomed to a cooler temp. to sleep. I tried leaving the temp steady for the last two days.

As I said in my original post. The furnace & HP seems to work OK. It`s the thermostat that orchestrates how when each one is called up.