Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : lennox heat pump,no heat
ed ray
02-08-05, 10:00 PM
came home today and the house was cold.inside fan is blowing, outside unit is comming on,or at least the fan is.checked the breakers,ok. checked the fuses both inside and out side with a dvom.no frost to be seen.emergency heat is working,noticeable diffrence in temp with emergency heat on.any suggestions? thanks
mattison
02-09-05, 07:55 AM
With your volt meter see if you have 24v to the outdoor contactor.
Ed Imeduc
02-09-05, 02:43 PM
You say out side unit fan came on. Did the compressor come on? The big copper pipe is it hot when the outdoor unit is running? can you be low on freon? What does it all do or run if you go over to AC on the tstat?
ED ;)
ED ;)
scottg
02-09-05, 03:59 PM
Well if you have an outdoor fan running then you probably have power to your compressor.
I suspect that the run capacitor is open or the compressor leads are burnt off at the compressor terminals.
If you have a amp meter then see if the compressor is drawing current on the common leg.
If it is not then interupt power to the unit and take off the compressor terminal cover and look at the terminals. If they look good then take a screwdriver and discharge the compressor run capacitor between herm and com. Then test the capacitance level at the same terminals and see if that coincides with the rating on the label of the capacitor.
One of these areas is where your problem lies.
I suspect that the run capacitor is open or the compressor leads are burnt off at the compressor terminals.
If you have a amp meter then see if the compressor is drawing current on the common leg.
If it is not then interupt power to the unit and take off the compressor terminal cover and look at the terminals. If they look good then take a screwdriver and discharge the compressor run capacitor between herm and com. Then test the capacitance level at the same terminals and see if that coincides with the rating on the label of the capacitor.
One of these areas is where your problem lies.
mattison
02-09-05, 07:17 PM
Doh. I missed the fan running part.