:confused: my boiler is not used for hot water 1 zone have a honey well triple aqua statrelay type Lb124a ,c L8151a the burner work well but the thermostat can not control the heat in the house replaced t stat still nothing the only way to control the heat is turning the main switch on & off the problem being that this creates very cold mornings or very hot nights any suggestions
Take the cover off of the aquastat and remove one of the wires on the T terminals. That is the wire from the thermostat. If the relay drops out and the pump stops, you have a pinched thermostat wire and need to run a new one or find the short. If the relay doesn't drop out post back and let us know what does happen.
Ken
joedeli
11-17-04, 01:38 PM
the t stat did not drop out when i took the wire off i can here the relay click when i turn up th t stat in the room could there be a short in thr taco 007-f5 circulator it has a yellow pack the wires run in to any help greatly app. thanks for your re ply while i'm sitting here i'm hearing a springing sound out of the circulator could it need to be replaced sorry i found my problem the aqua stat was wired for constant flow from the circulator thank again for the help :) :)