Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : heat pump problems
bob1968
11-07-04, 10:05 AM
i have a amana heat pump that is about 1yr old.......it worked fine last winter but this year i cant get the outdoor unit to come on at all......if i go out and engage the contactor manually it all come on and works fine as long as i hold the contactor in but that is a very good solution to my problem lol.......just a min ago i took a wire and jumped r and y together at the unit and the contactor engaged but when i pulled the jumper it disengaged
any help would be appreciated
thanks
any help would be appreciated
thanks
Ed Imeduc
11-08-04, 10:19 AM
Id start at the tstat first and see if R to Y there will pull it in If so can be the tstat if not then look at the wires.
For heat R -power Y -compressor G -fan and you can have O or B for the changeover valve or called the 4 way valve. You see you need all of them for heat. What works when you put it on cool??
;)
For heat R -power Y -compressor G -fan and you can have O or B for the changeover valve or called the 4 way valve. You see you need all of them for heat. What works when you put it on cool??
;)
hvac4u
11-09-04, 04:45 PM
tells us there is no call from inside on Y, could be stat, possibly, sounds like you need a pro unless you are comfortale with and have a volt meter
bob1968
11-10-04, 10:55 AM
ok i jumped the r and y at the tstat and still nothing at the outside unit......and yes i have a volt meter and use it quite often in my line of work.....i drill and service water wells for a living.....from household use all the way to city usage....so i am familiar with electricity
thanks
bob
thanks
bob
bob1968
11-10-04, 10:56 AM
oh and the outside unit dont come on with the cool either
Ed Imeduc
11-10-04, 05:57 PM
With the volt meter see if you have 24 Volts out there at the contactor When you have tstat on heat or cool and call for it. Can be its coil check this out next
.
ED ;)
.
ED ;)
heatpumpman
11-10-04, 07:02 PM
at the outside unit. Trace the yellow wire into the unit and all the way to the contactor.
hvac4u
11-12-04, 06:17 PM
there is a high pressure manual reset in that unit,
TURN POWER OFF FIRST
there was a problem with that switch's location as i recall, your installer should have the TM addemdum
good call heatpumpman
TURN POWER OFF FIRST
there was a problem with that switch's location as i recall, your installer should have the TM addemdum
good call heatpumpman
bob1968
11-21-04, 10:12 AM
man i feel like a complete fool........first i want to thank all of you for your advice and help.......i traced the yellow wire to the reset button....darn near need to take the whole unit apart to get to the reset button....i pushed it and voila it now works.....i have been using emergency heat for 3 weeks because of a 10cent reset....
thanks
ps. is there a reason or fault that the reset needed to be reset
thanks
ps. is there a reason or fault that the reset needed to be reset
Ed Imeduc
11-21-04, 10:19 AM
Could be high head---- but why???? fan not come on dirty coil out side or inside. filter clean?????
ED ;)
ED ;)
hvac4u
11-21-04, 11:21 AM
as i recall the position of the switch was faulty, causing nuisance trips
but then again be sure the coil is clean and the fan spins freely
but then again be sure the coil is clean and the fan spins freely