Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : Capacitor and Motor Starter


inspira
06-01-03, 10:14 AM
How do you check out a capacitor and motor starter on an A/C Condensor Fan Motor to determine if they are good?


GregH
06-01-03, 11:45 AM
inspira:

You can use a voltmeter to check for 24 volts at the coil if its not energizing and for 240 volts at output terminals if the contacts have pulled in. Also if the contacts have pulled in you can probe both terminals on the same line to check for an open or dirty contact.

Check a capacitor with an analogue ohmmeter. After turning off the power, short the two terminals to discharge residual power then probe both terminals with the meter set to about 1k ohms.
If ok the meter will rise slightly while charging and then dip back to zero. If the meter rises and stays the cap is shorted and if it doesn't move it could be open. Short the terminals to discharge when repeating the test.

inspira
06-02-03, 05:47 AM
Thanks for the info.....that was quite helpful.....need proper tools before continuing............:)