Gas and Oil Home Heating Furnaces - strange problem.....

Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : strange problem.....


pestguy54
04-08-03, 05:28 PM
i have had 3 ac guys out and of course my system never acts up when they here. so maybe someone can steer me in the right direction.live in chattanooga tenn and i have a split system. 2.5 ton lennox that is 9 years old. it has had its share of problems inc. a compressor that had to be replces at 2 years age. what it is doing is intermittent but has been doing it for almost 8 months. does it when it is 25 or 75 degrees. the fan will run fine for maybe 30 mins or so and will cycle normal. then the fan will run for maybe 1 min then stop come right back on and run for several mins. it will do this for as lond as we can stand it. will turn it off and after 30 mins or so will turn it back on and it may do the same thing or not. at other times it will run fine for weeks then start up again. it heats and cools fine but when it does this the lights blink like it is trying to cut off and it does sound like it. dont know what else to add except ask me and i will answer it. help steer me please...


410a
04-08-03, 07:03 PM
Tell us more.

Which fan? Indoor? Outdoor?

Gas heat? Electric Heat? Heat Pump? Geo?

GregH
04-08-03, 09:35 PM
pestguy54:

I may have an idea what the problem is but to be sure we need more info.
If you read: http://forum.doityourself.com/showthread.php?s=&threadid=122673 , what we need to know is here.


pestguy54
04-09-03, 06:21 PM
sorry guys. it is the outdoor fan and it is a heat pump.

GregH
04-09-03, 10:06 PM
pestguy54:

There is a good chance you have a bad condenser (outdoor) fan motor.
It may be running for a while and then overheats and shuts down. This will cause the compressor to overheat and short cycle.
If you shut off the power and remove the fan guard you can check the motor shaft by trying to move it from side to side. There should be no noticeable movement.
If not a bad shaft bearing then it could be the run capacitor or bad windings.
Check the motor and let us know.

410a
04-10-03, 05:49 AM
With the power turned OFF. I have seen this happen when the wrong size run capacitor is used. The motor nameplate will specify a run capacitor. Then check the capacitor installed. If the wrong size, change it. If uncomfortable with electricty, hire a pro.