Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.




View Full Version : zone valve problem?


redbeard266
01-25-03, 05:00 PM
I have a gas fired hot water baseboard heating system. It is split into 2 zones. The #1 zone for the first floor and the #2 zone for the second floor. When the tstat is turned up for the first floor the heat comes on instantly. When the tstat is turned up for the second floor we get no heat on the second floor. Any help with this problem would be great.


bigjohn
01-25-03, 06:22 PM
Well, since you said zone valve, I'll assume that's what you have instead of cirulating pumps. Locate the zone valve for the second floor and, using your voltmeter, see if you have 24 volts coming to the valve operater. If yes and the valve won't open, replace the valve. If no, trace the wiring back unitl you find why there is no power to the zone valve.

redbeard266
01-25-03, 07:09 PM
i have one circulating pump and two zone valves....gas hot water baseboard system..i also can't seem to locate any bleeder valves in zone 2