Doityourself.com community forum was created to provide answers to all questions related to home improvement and home repair. Doityourself community can help you find information about how-to topics on small fixes to large remodeling projects. With comprehensive how-to content and expertly moderated community forums DoItYourself.com makes it easy to tackle even the most complex home improvement projects.View Full Version : 2 zone valves on 1 ZV Controler circuit
PipeBender
12-05-02, 06:38 AM
Is it possible (recommended) to connect two Zone valves to one "circuit" on the Zone valve controller?
I have a situation where I would like two zones to activate from one thermostat. I am using the Taco zv406 control and Taco Gold Series Zone valves.
I have a situation where I would like two zones to activate from one thermostat. I am using the Taco zv406 control and Taco Gold Series Zone valves.
GregH
12-05-02, 11:07 AM
PipeBender:
Please read the Before Posting announcement and come back with a more detailed question.
Please read the Before Posting announcement and come back with a more detailed question.
PipeBender
12-05-02, 11:46 AM
I am not sure how much more info GregH wants. I did read the "Before Posting Announement".
However I will try to give you more info. The Taco Controler has four zone circuits. Normally you conncet one thermostat to one side of the circuit and a zone valve to the other side of the circuit.
What I would like to do is connect two zone valves to the bottom side of the circuit.
The Zone valves are rated at 24 volts .9 amps The contoler performance specifications says "All Zone Valve Controls are relay type DPDT and have a single phase motor rating per zone of
1/6 hp (5 A) @ 120 VAC.
However I will try to give you more info. The Taco Controler has four zone circuits. Normally you conncet one thermostat to one side of the circuit and a zone valve to the other side of the circuit.
What I would like to do is connect two zone valves to the bottom side of the circuit.
The Zone valves are rated at 24 volts .9 amps The contoler performance specifications says "All Zone Valve Controls are relay type DPDT and have a single phase motor rating per zone of
1/6 hp (5 A) @ 120 VAC.
GregH
12-05-02, 06:03 PM
PipeBender:
Thanks for the extra info.
I'm not familiar with that controller, but if the switching is by a DPDT relay, I can't think of a reason that it wouldn't work.
Thanks for the extra info.
I'm not familiar with that controller, but if the switching is by a DPDT relay, I can't think of a reason that it wouldn't work.
PipeBender
12-06-02, 06:27 AM
I have written to Taco (the manufacturer of the valve and controller) and will post what ever they send me. However if anyone else has any input on this it would be appreciated.
PipeBender
12-10-02, 02:41 PM
Just got an answer from Taco. You may put 2 valves on one zone; however you cannot exceed the total number of valves that the control was designed for. With 2 valves on one zone you will have one empty zone.
They also included a sketch of how this should be wired. I will try to describe it.
From the Zone Valve Controller (ZVC) Valve terminal block (VTB)Wire position 1 to position 1 of zone valve A (VZ-A), wire position 2 of VTB to position 2 of VZ-A, wire position 3 of VTB to position 3 of Zone Valve B (ZV-B). Finally, wire position 3 of ZV-A to position 2 of ZV-B.
They also included a sketch of how this should be wired. I will try to describe it.
From the Zone Valve Controller (ZVC) Valve terminal block (VTB)Wire position 1 to position 1 of zone valve A (VZ-A), wire position 2 of VTB to position 2 of VZ-A, wire position 3 of VTB to position 3 of Zone Valve B (ZV-B). Finally, wire position 3 of ZV-A to position 2 of ZV-B.
GregH
12-10-02, 04:04 PM
It's very much appreciated.